ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat Box
Recent Posts
Look at this mess...
by Trumpy - 11/07/19 11:48 PM
Fire source!
by sabrown - 11/07/19 08:39 AM
Parallel Conductor Divisor
by LongRunner - 11/04/19 02:21 AM
FPE in Germany
by Texas_Ranger - 10/29/19 05:12 AM
Mistake in Instructions?
by gfretwell - 10/28/19 06:36 PM
New in the Gallery:
FPE Breaker panel in germany
What is this for?
Who's Online Now
0 registered members (), 8 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
S.P. switching of 2P #220311 09/28/19 10:54 AM
Joined: Apr 2002
Posts: 186
T
triple Offline OP
Member
What are the limits (if any) of switching a 2-pole load with only one of its poles? Perhaps, if it is an automatic control then it is ok but if it is manual then it is not allowed? Also, does it matter if the single pole switching device is on the unit or in a remote location? For example, a 240v baseboard, electric heater may have a single pole, line-voltage thermostat (either on the heater itself or on the wall). However, take a 208 or 240v, single phase pole-light. Can I control it by a single-pole photocell on a nearby building (no 2-pole contactor or relay in between)? If so, why could I not also have a manual override switch that breaks only one line? Understand that I personally would not do either of these things and consider it "bad practice" whether it is code-compliant or not. Also, anything requiring an actual disconnect would need the breaking of all phase conductors but that is not a case I am considering.

2017 / 2014 NEC & Related Books and Study Guides
Re: S.P. switching of 2P [Re: triple] #220313 09/28/19 12:51 PM
Joined: Jul 2004
Posts: 9,411
G
gfretwell Offline
Member
The way I read it you can use a single pole device for control but you still need a 2 pole device for a disconnect anywhere one is required or anything labeled "off".


Greg Fretwell
Re: S.P. switching of 2P [Re: gfretwell] #220314 09/28/19 01:34 PM
Joined: Apr 2002
Posts: 186
T
triple Offline OP
Member
Good point. I didn't think of the fact that the switch may (but not necessarily) state "off" on it. For instance, a decorative style switch would not and there could not be many circumstances where a pole light requires a disconnect. It still seems as though the code has dropped the ball if a s.p. decora switch is allowed here.

Re: S.P. switching of 2P [Re: triple] #220315 09/28/19 07:22 PM
Joined: Jul 2004
Posts: 9,411
G
gfretwell Offline
Member
I think the exception is more limited than simply allowing anything to be OK. These are in individual articles on specific pieces of equipment like 424.20(B)

Quote

(B) Thermostats That Do Not Directly Interrupt All Ungrounded
Conductors. Thermostats that do not directly interrupt all
ungrounded conductors and thermostats that operate remotecontrol
circuits shall not be required to meet the requirements
of 424.20(A). These devices shall not be permitted as the
disconnecting means.


Greg Fretwell
Re: S.P. switching of 2P [Re: triple] #220316 09/28/19 08:01 PM
Joined: Jul 2004
Posts: 9,411
G
gfretwell Offline
Member
Your single pole switch to a lamp is outlawed here

Quote
410.93 Double-Pole Switched Lampholders. Where supplied
by the ungrounded conductors of a circuit, the switching
device of lampholders of the switched type shall simultaneously
disconnect both conductors of the circuit.


Greg Fretwell

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
BigB 5
andey 2
NORCAL 1
Popular Topics(Views)
260,573 Are you busy
195,404 Re: Forum
184,738 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3