If I have a j box in the basement where all branch circuits end..and need to extend four feet through foundation to panel

Is there a derating requirement from the j box to the panel based on length?


Don't drive and TEXT! Drive now TALK LATER!
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
24" of grouped conductors starts kicking off derating. In #12 and #14 using 90c conductors you are usually not in trouble until you get 9 in a pipe.