Derating length requirements #220296 09/24/19 04:26 PM
Joined: Jun 2012
Posts: 74
akmaster Offline OP
Member
If I have a j box in the basement where all branch circuits end..and need to extend four feet through foundation to panel

Is there a derating requirement from the j box to the panel based on length?


Don't drive and TEXT! Drive now TALK LATER!
2017 / 2014 NEC & Related Books and Study Guides
Re: Derating length requirements [Re: akmaster] #220298 09/25/19 12:54 AM
Joined: Jul 2004
Posts: 9,623
G
gfretwell Online Content
Member
24" of grouped conductors starts kicking off derating. In #12 and #14 using 90c conductors you are usually not in trouble until you get 9 in a pipe.


Greg Fretwell

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 10
Trumpy 7
Popular Topics(Views)
279,176 Are you busy
212,237 Re: Forum
199,252 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3