I ask because I got this question wrong:
"You need three over load units for a normal 3 phase AC motor."
True or False
Answer: "Yes 430.27"
Does a 'normal 3 phase AC motor' include capacitors?
My background is shipping and that is not normal from my experience, perhaps with small HP motors only.
My answer was False based on this code trace:
430.37(Ex) --> Table 430.37(Ex)
430.111
430.32
240.15
240.84
What's your thoughts?
Thanks,
Phil
Where ever you go, there you are.
Since here is a phase displacement in 3 phase motors they do not need a capacitor to start. The function of the capacitor is to create phase displacement and create a magnetic field to "chase" on a single phase motor. Once it gets spinning the rotating field is created within the windings. Thank you Mr Tesla.
Hi,
Yes, I get why the capacitor is needed for starting and phase rotation.
I'm still not getting this question and answer though. What am I missing here?
Why is the given answer True, due to the need for capacitors on a 3Ø motor?
Perhaps this is a typo in the answer and the code should be 430.37, not .27.
Question:
True or False
Code
430.27 Capacitors with Motors. Where capacitors are installed in motor circuits, conductors shall comply with 460.8 and 460.9.
Code
460.8 Conductors.
(B) Overcurrent Protection. An overcurrent device shall be provided in each ungrounded conductor for each capacitor bank. The rating or setting of the overcurrent device shall be as low as practicable.
Exception: A separate overcurrent device shall not be required for a capacitor connected on the load side of a motor overload protective device.
Thanks,
Phil
True or False
Is it me having a brain freeze, or are not 'overloads' what us older guys called 'heaters'? What does the verbage within the question have to do with capacitors.??
Seems like the conversation is leaning towards capacitors that are installed for power factor correction reasons!
I see what happened, There is a typo in the code reference. They really mean table 430.37