ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat Box
Recent Posts
Look at this mess...
by Trumpy - 11/07/19 11:48 PM
Fire source!
by sabrown - 11/07/19 08:39 AM
Parallel Conductor Divisor
by LongRunner - 11/04/19 02:21 AM
FPE in Germany
by Texas_Ranger - 10/29/19 05:12 AM
Mistake in Instructions?
by gfretwell - 10/28/19 06:36 PM
New in the Gallery:
FPE Breaker panel in germany
What is this for?
Who's Online Now
2 registered members (Scott35, sabrown), 6 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Wire size #220057 05/02/19 05:29 PM
Joined: Mar 2005
Posts: 233
watersparkfalls Offline OP
Member
If you have a hydronic heat pump with a minimum ampacity of 23 amps and max of 35 amps wired with mc...wouldn’t sizing the wire to max current make the most sense? Has anyone ever had a problem with sizing motor to minimum ampacity before? Probably should have worded as a code question.

Thanks,
H20

2017 / 2014 NEC & Related Books and Study Guides
Re: Wire size [Re: watersparkfalls] #220060 05/02/19 09:34 PM
Joined: Jul 2004
Posts: 9,411
G
gfretwell Offline
Member
The bottom line is, "what does the label say" . You don't need to wire any motor load for the locked rotor current because it is only there for a second or less. We wire for 125% of the full load amps. In a complex box like an HVAC system the industry engineers evaluate that box and give you a label for guidance. As an electrician or inspector we should just believe. You can use a #12 for that if everything is rated 75c (breaker, conductors and HVAC lug)


Greg Fretwell
Re: Wire size [Re: gfretwell] #220094 05/27/19 09:35 PM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
I agree with Greg with one exception.
Fire pumps are wired differently because they are expected to run to destruction rather than trip on normal overloads like a regular motor.
The wire sizing is capable of carrying LRA for 20 seconds or more since the motor may have issues getting up to speed.
Nobody wants to console the owner of a burning building by telling them "hey...at least the fire pump motor got tripped offline and is still okay".


Ghost307

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
BigB 5
Trumpy 1
Popular Topics(Views)
260,581 Are you busy
195,414 Re: Forum
184,747 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3