Residential Smoke wiring #219892
01/07/19 09:46 AM
01/07/19 09:46 AM
S
Steve Miller  Offline OP
Member
Joined: Aug 2001
Posts: 329
Bruceton Mills, WV
We have always advocated wiring the smokes to a local lighting circuit. The thinking is that if the breaker trips, you'll know it. You may not know it if a dedicated smoke circuit trips. Example being ... residents are on vacation and a surge or short outage causes the breaker to trip. After a week or so the batteries are dead and the residents return unaware of the lack of protection. The question: (I have no access to NFPA 72) is this code or just something we have always done?

Work Gear for Electricians and the Trades
Re: Residential Smoke wiring [Re: Steve Miller] #219897
01/08/19 01:56 PM
01/08/19 01:56 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,063
Brick, NJ USA
A quick discussion with my Fire Official results in:

Yes, the smokes on a circuit with a light (luminaire) WAS the chosen way, back 20-25 years.

NOW, a dedicated circuit is required. It's in "72", but neither one of us has the time to hunt it down.

BTW, Bob has 40+ years in Fire.


John
Re: Residential Smoke wiring [Re: Steve Miller] #219898
01/08/19 02:00 PM
01/08/19 02:00 PM
S
Steve Miller  Offline OP
Member
Joined: Aug 2001
Posts: 329
Bruceton Mills, WV
Thanks

Re: Residential Smoke wiring [Re: Steve Miller] #219903
01/10/19 07:55 AM
01/10/19 07:55 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,063
Brick, NJ USA
Steve

Documentation I have access to (Thanks Bob) is as follows:

NJ IRC 2015......R314.6 .....Wiring shall be permanent, and without a disconnecting switch other than those required for overcurrent protection.

2013 National Fire Alarm & Signaling Handbook Chapter 29

Basically says a good practice is to use a branch circuit that supply a lighting circuit.....Further into that text it alludes that some states & locals may require a dedicated circuit, consult AHJ. (Not complete text, as I am not a typist.)

Seems like a round about way of saying 'either or'; however here it is a dedicated circuit.


John
Re: Residential Smoke wiring [Re: Steve Miller] #219904
01/11/19 12:36 AM
01/11/19 12:36 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,335
Estero,Fl,usa
Put it on the circuit with the Wi Fi router. They will track down the fault right away. wink


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 