1-1/4 in EMT #1 THHN Table C4 allows 4 conductors. This exceeds the 40% fill limit per Table 1 Why is this allowed?


George Little
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,919
Likes: 30
G
Member
Dunno, when I run it I get 1.59 sq in and a 1.25 EMT is 1.50
Didn't someone just tell me NFPA was infallible wink