Pull out fuse panel? #219828
12/04/18 11:41 AM
12/04/18 11:41 AM
C
cgw  Offline OP
Member
Joined: Jul 2004
Posts: 134
Rochester NY
Correct me if I am mistaken:
1. The photo below is a fuse panelboard.
2. Replacement fuses are common and obtainable.
3. The panelboard is safe.
Any other comments?


[Linked Image]

Work Gear for Electricians and the Trades
Re: Pull out fuse panel? [Re: cgw] #219830
12/04/18 12:07 PM
12/04/18 12:07 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,323
Estero,Fl,usa
Yes
Yes
Depends.
That is a cartridge fuse panel using pull out fuse holders. The fuses are available and usually in a lot of values you can't find in a breaker but they may not be cheap.
Safety really depends on the condition of the panelboard. If everything is in good condition some say fuses are safer than breakers but not as convenient.


Greg Fretwell
Re: Pull out fuse panel? [Re: cgw] #219835
12/05/18 12:42 PM
12/05/18 12:42 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,050
Brick, NJ USA
If it's in good shape, leave it alone, as Greg said.

A little sanding, and a coat of paint on the cover maybe?

I have a few friends who worked for Bussmann, and they have always professed what Greg added that fuses are superior to CBs. They had some great videos to sway people, specially for fault conditions.


John
Re: Pull out fuse panel? [Re: cgw] #219836
12/05/18 03:34 PM
12/05/18 03:34 PM
G
geoff in UK  Offline
Member
Joined: Dec 2002
Posts: 194
UK
My belief is that fuses are best for short circuit protection, but not so good for overload protection. Conversely circuit breakers are best at overload protection.

Re: Pull out fuse panel? [Re: cgw] #219837
12/05/18 07:48 PM
12/05/18 07:48 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,323
Estero,Fl,usa
It is pretty much impossible to have a fuse fail "closed" and when they change value, it tends to be toward a lower rating. We used fuses a lot in the computer business because they offered better protection for the hardware. You can also get them in just about any rating you like. The main flaw is it is too easy to replace a fuse with a larger size than the specifications.
I had a problem with an installation many years ago and there was nothing I could do about it. This was a big rest stop on the interstate with toaster wire heat along with a lot of other load. They served it from a 400a fused service disconnect and the feeder to the building where they had a 400a panel was fed by 300 Kcmil aluminum. I said the wire was too small and they said they only had 225a fuses in the service disconnect and everything was legal.
They also said the 400a breaker in the panel was just the building disconnect and the up stream fuses protected the feeder. After looking it up, they are right and I even talked to other inspectors. You have to inspect what is there, not the dumbest thing someone might do later. I wrote a proposal, more to get the sense of NFPA than to actually get a code change and their attitude was the same. We have to trust that there will be qualified professionals working on these things and the fuses installed determine the minimum ampacity of conductors, not the biggest standard fuse that will fit. My problem is this will be serviced by DOT workers, not electricians. They will use what they have on the truck. I did make them label the disconnect "225a fuses only" since they said that was all they needed.


Greg Fretwell
Re: Pull out fuse panel? [Re: cgw] #219838
12/06/18 02:12 AM
12/06/18 02:12 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,253
SI,New Zealand
What does it look like if you take the dead-front off?
Things like this tend to hide "secrets" laugh

Re: Pull out fuse panel? [Re: cgw] #219846
Yesterday at 05:09 PM
Yesterday at 05:09 PM
W
wa2ise  Offline
Member
Joined: Nov 2002
Posts: 788
Oradell NJ USA
My house's service entrance uses a fused service equipment panel
[Linked Image]
Closeup of the stickers:
[Linked Image]

It was installed in the early 1950's. When 100A was a big service. Spares sitting behind the meter, but never had to use them.
"Aug 9 '76 failure" was a big blackout in my town... smile


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 7,050
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,227 Are you busy
189,197 Re: Forum
178,880 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 15 (0.003s) Memory: 0.9873 MB (Peak: 1.1466 MB) Zlib enabled. Server Time: 2018-12-16 01:12:51 UTC