NEC 230.95 GFPE on 1KA WYE Services

Whats the reasoning on the GFPE on 1KA solidly grounded WYE services and not other configurations.

It was put in the code in 71', Free Access doesn't have 71' comments, do any of you?

Thanks.

Last edited by Wiresmith; 11/28/18 06:36 PM.
Horizontal Ad
Joined: Jul 2004
Posts: 10,004
Likes: 36
G
Member
Delta might be impedance grounded or perhaps not grounded at all?



Greg Fretwell
Joined: Apr 2018
Posts: 19
W
Member
Originally Posted by gfretwell
Delta might be impedance grounded or perhaps not grounded at all?


so could wye, and they say "SOLIDLY GROUNDED wye", not just solidly grounded

i did run across a study that suggested grounded wye secondary configuration faults have higher fault current, but i think that would make the grounded wye having less of a need for GFPE because the GFPE in my mind is for lower current fault or pulsing, the higher available current should be more likely to open the OCPD under ground fault conditions


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Top Posters(30 Days)
Popular Topics(Views)
337,600 Are you busy
262,958 Re: Forum
243,233 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5