#219711 10/16/18 02:04 PM
Joined: Jan 2005
Posts: 91
H
Member
It's been awhile since I worked in a Class 2, Div 1 area and I need to select an enclosure for a PLC and an HMI. Any thoughts on which enclosures would fit the bill here?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: May 2005
Posts: 984
Likes: 1
G
Member
Getting the PLC into a hazardous enclosure should solve one problem, but the HMI is going to be an issue.
Unless you can find an HMI that is listed for that environment (like the ones from HMI Elements or AIS) you're going to be stuck.
In order for an HMI to work you'll need to touch it so putting it inside an enclosure with its face exposed won't work very well.


Ghost307