ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
UL 508A SPACING
by ale348 - 03/29/24 01:09 AM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (ale348), 302 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#219586 09/05/18 08:50 AM
Joined: Mar 2003
Posts: 849
Y
Member
Lights
9 400 watt lights on circuit

9 x 400 = 3600 watts

3600 x 125% (continuous duty) = 4500

4500 divided by 240 -= 18.75 amps

to close for 20 amp breaker?????

Could you jump wire up to #10 & put 25 amp breaker?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Mar 2003
Posts: 849
Y
Member
I'm getting this idea off 210.23 (c) 30 amp branch circuits (( 2014 NEC page 70-59.))

There are 9 plug connected 400 W fixtures on this circuit.

If can use the 30 amp rule =1 circuit two pole brk 25 amp
if not = 2 circuits two two pole brk 20 amp

Yoopersup

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
You have already taken into account the 80% factor. It should be fine on a 20 with #12. The only issue might be inrush if this is an inductive load.


Greg Fretwell
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Yoop:

You may want to check the spec on the fixture/ballast. You didn't say if MH, or HPS, or ??

MH 400 watt is 460 watts +/- operating current.





John
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
Good catch John. If that is true it does take you over the 16a max on a 20a circuit so you will be on a 25/30 or split it between 2 circuits for a little redundancy.


Greg Fretwell
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
As the EC, I would do 2 circuits, 20 amp @ 240 volt. I did a lot of lighting as an EC back in the day, both interior and site lighting. A lot of design/ build, retrofit HPS to MH (no LED back then) . We even eliminated LPS site lighting.

Yoop has 9 fixtures, probably 3 rows of 3 ea., so a 5/4 split would not be bad, one row of 3 with the center of the next row, then the balance of 5.

I wonder IF he considered LED, or T-5 high bays??

There's a lot of LED retro going on here, and I'm amazed at the rapidly changing technology. I just started plan review today on some crazy 'arcade' in a mall, and it is 99% LED. A recent Apple retail store is 100% LED, with a gorgeous evenly lit ceiling in the whole retail area.


John
Joined: Mar 2003
Posts: 849
Y
Member
The total area is 6 rows of 9 Green house grow lights.

They want to be able to put each row on a time clock.

Led lights (which I brought up) four or more times the cost

Additional Info .

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
If John is right about the total load (ballast plus lights = 4600w) your original plan may be the way to go (25a/ 10ga wire). If you find out it is really only 400w per luminaire, you can do 20a / 12ga.


Greg Fretwell
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Greg:

As I do not have all the catalogs I used to have in my home office, and this is 'bugging' me, I found this limited info today.

https://unvlt.com/pdf/literature/navigator/pdfs/BNC_Sect_4_HID.pdf

Hopefully this paste job comes up as a link to ballast info.

The good info is on page 4-17, 'input watts'!


Last edited by HotLine1; 09/10/18 01:42 PM. Reason: add page info

John
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I see that. It appears that all of those lights carry an overhead beyond the nominal watt rating of the light. My only question is whether the "max amps" is the initial starting current or the continuous load once they start and settle down. That would make a difference when you were calculating the continuous load.


Greg Fretwell
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Greg:

From memory, HPS had a lower 'running' current after warm up; MH was the opposite.

There are 360 watt MH lamps, which were supposed to retro the 400 fixtures for 'energy saving'. I do not know what this did/does to the operating load. Comparative math (seat of the pants style) 10% reduction in lamp wattage should equate to 10% on line side of ballast; 460 -46 = 414.

Time to do the upsell to T5 fluorescents, or better yet LED with 100k hr life. ROI is quick too.


John
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I don't know how well LED grow lights work. I suppose it depends on the wave lengths of the energy plants absorb in the various magical processes that take place. LEDs tend to be monochromatic.


Greg Fretwell
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
A EC mentioned at a recent seminar that he completed a medical grow building with LED fixtures. The fixtures were supplied by the grower.

I think the fixtures were within the spec/plans that were submitted to the State for review and the jumping through hoops for the legal growers and dispensaries.

The discussion I had with him was these LEDs were within the spectrum for grow lights. That is a little beyond my scope.


John
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Yoop:

Sorry if I’m getting off the path of your original question.


John
Page 1 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5