#219466 07/24/18 10:55 AM
Joined: Mar 2003
Posts: 849
Y
Member
Grounding conductor to water line & building steel with 6 - 600 mcm per phase.

per 250.66 = 3/0 copper. Just checking .

2500 amp service

Yoopersup

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Apr 2002
Posts: 7,380
Likes: 7
Member
Check!

Unless the specs indicate a larger size, as some engineers get carried away.


John