Re: Tray cable? [Re: gfretwell] #219450
07/11/18 07:45 PM
07/11/18 07:45 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,041
Brick, NJ USA
The Rome’s is still NG outside, in Carflex or whatever.

BTW, what is that 2x4 wood framing? Interior door (closet or room). Looks like the 2x don’t make it all the way up, or are they adding more? Is that 1x a header? Also interesting is the method of attachment of the top and uprights. Looks like they notch overlap, as opposed to the uprights being inside the top plate.


John
2017 / 2014 NEC & Related Books and Study Guides
Re: Tray cable? [Re: gfretwell] #219455
07/11/18 09:18 PM
07/11/18 09:18 PM
G
gfretwell  Offline
OP
Member
Joined: Jul 2004
Posts: 9,306
Estero,Fl,usa
The wood is just for the door frame so they have a place to screw in the hardware and nail in the casing.
They are inside the C channel on top. Maybe the picture is not clear on that.
I agree on the NM, no matter how they hide it. The strange thing is the tray cable would be legit. "In a raceway" is one of the accepted uses in 336.10. I am just not sure how they would have to continue on once they got inside. I suppose they might terminate the NM in the disconnect on the wall. That makes is sort of legal. It is about like feeding the jelly jar next to the door or a surface mounted FS receptacle box outside.
My bet, they strip the jacket and pull it through the Carflex, pretending it is THWN.


Greg Fretwell
Re: Tray cable? [Re: gfretwell] #219464
07/23/18 06:02 PM
07/23/18 06:02 PM
S
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 610
massachusetts
Tray Cable marked with TC-ER is not listed for interior use without a raceway or cable tray system...see 336.12(2)

But...according to 336.10(9), tray cable IDENTIFIED for use in 1 & 2 family dwellings is allowed...this cable is said to be marked with TC-ER-JP

JP for joist pull.

Re: Tray cable? [Re: gfretwell] #219465
07/23/18 09:40 PM
07/23/18 09:40 PM
G
gfretwell  Offline
OP
Member
Joined: Jul 2004
Posts: 9,306
Estero,Fl,usa
It is an interesting product. I never really saw it before. The stuff I saw was not marked JP. That could make a serious dent in the NM and UF market.


Greg Fretwell
Re: Tray cable? [Re: gfretwell] #219683
10/02/18 05:57 PM
10/02/18 05:57 PM
S
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 610
massachusetts
Hi guys...the TC-ER cable is a Tray Cable and can not be used inside a building unless in cable tray or a raceway. That TC-ER cable was supposed to pick up a listing for use in 1&2 family dwellings in accordance with 2017 336.10(9) with a new marking "JP" for joist pull. So you would see TC-ER-JP...but I have not seen any of it on the streets.

There is a product in the supply houses around here that some are starting to use...

Here is a link...

https://www.houwire.com/pdf/14-04DUCKT-STRIP.pdf

shortcircuit

Re: Tray cable? [Re: gfretwell] #219687
10/02/18 07:04 PM
10/02/18 07:04 PM
G
gfretwell  Offline
OP
Member
Joined: Jul 2004
Posts: 9,306
Estero,Fl,usa
I was surprised to see the TC cable. It was the first time I had ever seen any on a roll and I helped myself to a few inches of it, just for a look. They were using it for the LV on a minisplit.
I really see no reason why it would not take over the NM and UF market tho.


Greg Fretwell
Page 2 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004