ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 228 guests, and 10 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#219422 06/27/18 09:02 AM
Joined: Mar 2003
Posts: 849
Y
Member
I take it calculations are Calculations HV or LV .
Calculators on line seem to work for both HV & Medium voltage.
Any one know any different.Or have link to HV Calculators???
I know terms are 90c not 75c And cable amperage of cable different .
Thank you .
Yoopersup

Example below
1 conductors per phase utilizing a #3/0 Copper conductor will limit the voltage drop to 1.76% or less when supplying 200.0 amps for 8000 feet on a 13800 volt system.
For Engineering Information Only:
200.0 Amps Rated ampacity of selected conductor
0.077 Ohms Resistance (Ohms per 1000 feet)
0.042 Ohms Reactance (Ohms per 1000 feet)
345.0 volts maximum allowable voltage drop at 2.5%
242.798. Actual voltage drop loss at 1.76% for the circuit
0.9 Power Factor

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
Voltage drop is dependent on the current not the voltage so the calculator will still work but obviously the percentage is based on the voltage you start with.