ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Video door bell causing chime activation of coil
by gfretwell. 12/10/18 12:35 AM
Conduit fill Calculations
by gfretwell. 12/08/18 08:39 PM
Pull out fuse panel?
by Trumpy. 12/06/18 02:12 AM
Swimming Pool question
by HotLine1. 12/05/18 12:37 PM
Tingle off the water spigot
by rmiell. 11/30/18 01:03 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 27 guests, and 25 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
GFCI Dish Washer & Food Disposer #219230
04/06/18 11:14 AM
04/06/18 11:14 AM
T
Tom_Horne  Offline OP
New Member
Joined: Dec 2017
Posts: 1
Montgomery County Maryland
I just went through re-inspection because the under sink receptacles for the food waste disposer & Dish Washer did not have GFCI protection. NEC addition being applied is the 2Ø14 one because of when the Building Permit was issued. I realize that having been retired for 2 code cycles I may have missed the change but I have never heard of such a thing. Can anyone help me out with the code reference for this requirement? I have been wrong before and I will be wrong again but this one threw me for a loop. I have been reading the Mike Holt site for the list of changes. Did I miss this one? Any help is appreciated.

--
Tom Horne

2017 / 2014 NEC & Related Books and Study Guides
Re: GFCI Dish Washer & Food Disposer [Re: Tom_Horne] #219231
04/06/18 01:05 PM
04/06/18 01:05 PM
HotLine1  Online Content

Member
Joined: Apr 2002
Posts: 7,050
Brick, NJ USA
The answer is within 210.8 (D) for the dishwasher.

Now, the disposal is ' opinion' or how one reads.....

" All Receptacles within 6' (six feet) of the outside top edge of the sink" (210.8 (A) (7).

The wording does NOT state in any direction from the edge; so some feel that IF the receptacle is under the sink, within the base cabinet, t is within the zone.

Note that the commentary within the 2014 NEC Handbook (NOT Code) states that receptacles installed for disposals, dishwashers, trash compactors are not required for GFI protection. THIS IS contradictory to 210.8 (D) within the same Handbook as "Code". This was corrected in the '17 Handbook.

Also, some do not "see" 210.8 (B) that is "Other then dwelling units" regarding kitchen outlet GFI protection.


Last edited by HotLine1; 04/12/18 12:09 PM. Reason: Corrected typos

John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,171 Are you busy
189,160 Re: Forum
178,836 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 15 (0.005s) Memory: 0.9443 MB (Peak: 1.0599 MB) Zlib enabled. Server Time: 2018-12-12 21:07:37 UTC