Safest socket system for wet pottery studio? #219158
02/21/18 06:12 PM
02/21/18 06:12 PM
Jules69  Offline OP
New Member
Joined: Feb 2018
Posts: 1
I have found MK MASTERSEAL PLUS 13A 2 GANG SWITCHED SOCKET (98279) £49 for each double - to protect sockets in pottery studio. Some sockets not being used.. is it safe to just put cover plate over and use silicone sealant on unused ones in area where wet spillage is likely? Setting up a new professional studio.

Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Re: Safest socket system for wet pottery studio? [Re: Jules69] #219162
02/23/18 06:34 AM
02/23/18 06:34 AM
dsk  Offline
Joined: Jun 2014
Posts: 77
I guess the best would be something like what you see on this page: GFCI (RCD) on each outlet will result in only a local switch off in case of a faulty device, but it may cost some more. (Not mutch more if this page has realistic pricing) Ebay:

As I know the UK system you have pretty heavy fuses, and use smaller fuses in each socket, it should have been the European standard!

Good luck from Norway!


Re: Safest socket system for wet pottery studio? [Re: Jules69] #219176
02/27/18 01:26 PM
02/27/18 01:26 PM
Texas_Ranger  Offline
Joined: Dec 2001
Posts: 2,416
Vienna, Austria
In all honesty I wouldn't use BS1363 in a professional wet environment like that. How about blue CEE (caravan plug)? Obviously need to be on 16 amp radials instead of ring mains or 20 amp radials.

Silicone near electrical fittings is a bad idea if it's acid-curing silicone, the fumes eat up all copper.

Re: Safest socket system for wet pottery studio? [Re: Jules69] #219193
03/09/18 11:39 PM
03/09/18 11:39 PM
Trumpy  Offline

Joined: Jul 2002
Posts: 8,236
SI,New Zealand
I'm sorry, but we don't do DIY questions here at ECN, you need to engage the services of a qualified Electrician.
Even so, anything in a wet area needs to be permanently connected, with cable glands for the inlet and outlet sides and sealed to IP55 at least.

Silicone sealant is available in neutral-cure as well, Texas-Ranger, that acid stuff is only for roofing and sealing around plumbing exposures.

{I will lock this thread in 3 days}


2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman


Member Spotlight
Posts: 264
Joined: February 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Trumpy 5
Popular Topics(Views)
244,547 Are you busy
181,672 Re: Forum
171,719 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 15 (0.003s) Memory: 0.9596 MB (Peak: 1.0940 MB) Zlib enabled. Server Time: 2018-03-22 13:35:58 UTC