Solid state relay or not #219163
02/23/18 06:50 AM
02/23/18 06:50 AM
D
dsk  Offline OP
Member
Joined: Jun 2014
Posts: 85
Norway
Hi
We have a storage water heater (2kW) and I believe it will work well with a timer, and just heating during the night when the power is less expensive. (The power company has automatic reading of the meter every single hour) The power is less ekspensive from midnight to about 6 a.m.
I want to build a unit controlled by a clock and an extra thermo-relay to override the clock if the temperature falls to much.

I know this is more or less common in the USA so your experience is important for my project here in Norway. Pretty much are equal, the system here is nominal 230V yours are 240, it is single phase, and the frequency does not matter as long as I do not use a timer with a frequency depended motor.

I do not trust regular timer with a mechanical switch even when it is rated for 16A so does a solid state relay or a mechanical industrial relay be the most trust-able?
Or what would you use in your house if you should build it and not buy it?
Should I put in more functions? what and why?

Work Gear for Electricians and the Trades
Re: Solid state relay or not [Re: dsk] #219164
02/23/18 04:17 PM
02/23/18 04:17 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 958
Chicago Illinois USA
I would run some numbers first to see if the saving are worth the work.

Even if the water heater was running continuously you would only be able to save 12kWH.
Over here that would be around $1.20; and could be a lot less if the water heater cycled during operation as most storage water heaters do.


Ghost307
Re: Solid state relay or not [Re: dsk] #219168
02/24/18 02:58 AM
02/24/18 02:58 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
To answer the original question there are very capable SSRs I am running Opto22 45a SSRs on my spa heater that is basically a 5500w water heater element . They can be driven directly from CMOS but I usually put a little silicon transistor in there (2n2222 sort of thing)
You can do a lot of cool things with SSRs and they fit nicely in the square sided handy boxes.


Greg Fretwell
Re: Solid state relay or not [Re: dsk] #219169
02/24/18 04:13 AM
02/24/18 04:13 AM
D
dsk  Offline OP
Member
Joined: Jun 2014
Posts: 85
Norway
Thank you, both of you. The calculations are difficult but I have a lot of parts in the basement, parts I actually have no other use for so this will not be a fair calculation. To get confirmed that a SSR is good, for this is a positive feedback for the possibility to use a smaller cabinet. My main concern is to not increase the risk of failure. This setup will result in longer periods of full load, and if we have a weak point, that may be a risk of fire.

Our codes has been changed due to observations of hot connections, the old 16Amp (schuko) are not allowed for continuous loads as 2 kW water heaters in new buildings. In my house, this has worked for 30 years with no problems, putting in this modification, it will probably be vise to change that to a CEE 17 system, this is also used in USA.
http://internationalconfig.com/prod_shot/888-2126-NS.jpg

I remember those from the building of the Oakland bay bridge project. The only US job I ever has been involved in.

Re: Solid state relay or not [Re: dsk] #219170
02/24/18 05:52 AM
02/24/18 05:52 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
The only thing I will caution you about is a SSR will need a heat sink if you are running 10a through it. Plan on shedding about 7 watts. This is not a huge heat sink and the cabinet may be plenty. On my spa controller I am dealing with more like 11kw of load and that is around 16-17 watts each for 2 SSRs. They are screwed tight to the cabinet with heat sink goo and a finned heat sink is on the other side with the goo under it. The thing never gets more than slightly warm (35c or so in a 20c ambient)


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,431 Are you busy
188,034 Re: Forum
177,615 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.036s Queries: 15 (0.005s) Memory: 0.9702 MB (Peak: 1.1103 MB) Zlib enabled. Server Time: 2018-10-19 15:40:04 UTC