Load Calcs and tankless water heater #219119
02/01/18 08:40 PM
02/01/18 08:40 PM
B
BigB  Offline OP
Member
Joined: Mar 2004
Posts: 734
Tucson, AZ USA
Do you figure the water heater at 100% of it's full load KW rating? I have a customer with a 200 amp service. Present load calcs come to 123 amps without water heating. They want to add a Tempra 24KW tankless water heater. I know code doesn't care about occupancy but as a side note there is only one occupant.

Work Gear for Electricians and the Trades
Re: Load Calcs and tankless water heater [Re: BigB] #219120
02/02/18 02:04 AM
02/02/18 02:04 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,304
Estero,Fl,usa
What method did you use for the calc? You might squeak in with the optional method but I am not sure if it is the right thing to do.


Greg Fretwell
Re: Load Calcs and tankless water heater [Re: gfretwell] #219121
02/02/18 08:10 AM
02/02/18 08:10 AM
B
BigB  Offline OP
Member
Joined: Mar 2004
Posts: 734
Tucson, AZ USA
Originally Posted by gfretwell
What method did you use for the calc? You might squeak in with the optional method but I am not sure if it is the right thing to do.

Hi Greg,
I already did use the optional method

Re: Load Calcs and tankless water heater [Re: BigB] #219122
02/02/18 08:07 PM
02/02/18 08:07 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,304
Estero,Fl,usa
Quote
I already did use the optional method


That tends to be the most generous with big FIP loads so you might be looking at a service upgrade. That is not unusual with these electric tank less water heaters. Chances are they would never have a problem and an analysis of the other loads might give you better guidance but we tend to design for what might happen, not what usually happens. Think Christmas eve, everything in the kitchen is going, "Griswald" lights in the yard, heat is blasting, someone is in the spa and they turn on the hot water.


Greg Fretwell
Re: Load Calcs and tankless water heater [Re: BigB] #219123
02/02/18 08:30 PM
02/02/18 08:30 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,039
Brick, NJ USA
The solution up/over here has been a service upgrade to 400/320 amp. Most of the design professionals on new/reno SFDs with the instant/tankless units.

We had one McMansion, where the owner was asking for three (3) of the 24KW units, and had a POCO request for 600 amp, 3 phase, 4 wire 120/208 volt. There is a lot of POCO line work required, and that equals $$$$

IMHO, 24KW added to a 200 amp, with 123 amp calc load is a potential liability on you, IF you are doing the calcs, instead of a design professional. No intent made to insult your ability, but watch the liability.


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 68
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
Popular Topics(Views)
251,569 Are you busy
188,724 Re: Forum
178,437 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 15 (0.003s) Memory: 0.9697 MB (Peak: 1.1107 MB) Zlib enabled. Server Time: 2018-11-18 16:28:56 UTC