Is there a listed flat cable solution that can be used under a carpet. Amazon sells one but I do not see any reference to it being listed. I bumped into this on a homeowner BB and I did not address it. The object is to get a receptacle in the middle of a room without trenching the floor.
Greg Fretwell
|
|
|
|
Joined: Apr 2002
Posts: 7,409 Likes: 7
Member
|
Greg:
AFAIK, the onl listed use of flat carpet cable is under carpet tiles, not ‘one piece’ carpeting. (Commercial)
I guess one could request a variation from the AHJ. From my experience with tools, it is a PITA on the install. I last did it in a few offices for conference table locations in lieu of cutting the slab.
John
|
|
|
|
Joined: Oct 2000
Posts: 4,149 Likes: 4
Member
|
To me, this just doesn't seem like a good idea, even under carpet squares.
It always reminds me of when I worked for a Moving Company and we regularly had to wheel dollies with full double-wide File Cabinets across them. I don't know what they weighed, but I'm guessing over 1000 lbs. We did mostly put down sheets of Masonite to keep the squares from popping up, but I still think there might be a chance for cable damage below.
Bill
Bill
|
|
|
|
Joined: Apr 2002
Posts: 7,409 Likes: 7
Member
|
I don;t remember all the details, but it was an involved install, and that tenant was in and out in a few months & space was renovated.
There was a base of vinyl, the FCC, another layer of vinyl, and a roll of sheet metal over that, and then wide tape cover. It was 120 volt and data.
John
|
|
|
|
Joined: Jul 2004
Posts: 10,004 Likes: 36
OP
Member
|
Greg Fretwell
|
|
|
|
Joined: Apr 2002
Posts: 7,409 Likes: 7
Member
|
Nice product description in the link. One would think that a perfect translation into the English language would be mandatory when selling stuff..
This could be a fire waiting to start, UL?? You have to be kidding.
John
|
|
|
|
Joined: Jul 2004
Posts: 10,004 Likes: 36
OP
Member
|
You can see my concern. I suppose a product like this could be made but I am sure this is not it.
Greg Fretwell
|
|
|
|
Joined: Sep 2002
Posts: 946 Likes: 2
Member
|
324.12(4) states that flat conductor cable shall not be used in residential, school, & hospital buildings.
|
|
|
|
Joined: Oct 2000
Posts: 5,393
Member
|
324.12 Uses Not Permitted. FCC systems shall not be used in the following locations: (1) Outdoors or in wet locations (2) Where subject to corrosive vapors (3) In any hazardous (classified) location (4) In residential buildings (5) In school and hospital buildings, other than administra‐ tive office areas Looks like the '17 limited it's usage even more.....? ~S~
|
|
|