Cable Point of Entry #219010 01/10/18 12:55 PM
Joined: Jan 2018
Posts: 7
L
libellis Offline OP
New Member
The National Electrical Code definition of Point of Entry for fiber optic cable (NEC 2014, Article 770.2) states:

"The point within a building at which optical fiber cable emerges from an external wall, from a concrete floor slab, from rigid metal conduit (RMC), or from intermediate metal conduit (IMC)."

My question is if a conduit run that contains metal pull boxes is used to create a distant Point of Entry within a building, is this still code compliant, or are pull boxes not allowed?

I would think that it would still be compliant, otherwise a long conduit run without pull boxes could be impractical, but I don’t know if a pull box would be considered as exposing the cable. Code prohibits non fire rated cable from running more than 50’ exposed from the Point of Entry.

2017 / 2014 NEC & Related Books and Study Guides
Re: Cable Point of Entry [Re: libellis] #219011 01/10/18 01:27 PM
Joined: Jul 2004
Posts: 9,414
G
gfretwell Offline
Member
As a general rule you don't use the "definition" section to describe methods. That is just defining terms. Go down to section II in article 770 to read more about fiber entering buildings. (starting at 770.47)
If you look at raceways in Chapter 3 of the code you will see that boxes and conduit bodies are considered to be part of the raceway system if they are installed in the correct manner so that part of your question is "yes" they are allowed in that system.


Greg Fretwell
Re: Cable Point of Entry [Re: gfretwell] #219014 01/10/18 08:40 PM
Joined: Jan 2018
Posts: 7
L
libellis Offline OP
New Member
Much appreciated - that answer was right on target.

Article 770.48 was the motivation for my asking the question, but I didn't think of the Chapter 3 information regarding raceway components that you pointed out. Thanks.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 1
Popular Topics(Views)
261,161 Are you busy
196,296 Re: Forum
185,566 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3