Casino I take it under Article 518 Place of Assembly ??
No PVC inside unless encased in 2 inches concrete .(518.4 A)
518.4 B Non rated Construction only Exceptions. (Info from Building Inspector)
PVC over Dropped ceiling tile ceilings? (15 min . fire rating )
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
Yoopersup:
What you stated above is 'chapter and verse' out of the bible.
FWIW, I have not seen any jobs in places of assembly that used PVC or NM cable. The only PVC was within the floor slabs, and for the services.