How far away from an outdoor hot tub must a ceiling fan be? I thought it was 5 ft. but am having trouble finding it.
Thanks

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,919
Likes: 30
G
Member
Look at 680.22(C) as referenced in 680.42
The exclusionary "box" is 5 feet horizontally and 12 feet vertically from the closest point of the water.
There is an exception for existing lights and fans that lets you be 5' above the water level vertically but still not over the water.
This is from the handbook

[Linked Image from gfretwell.com]