Blackened bare copper in panel ? #218819
10/25/17 12:09 PM
10/25/17 12:09 PM
L
Lectricfishrman  Offline OP
New Member
Joined: Apr 2008
Posts: 6
Va.
Recently a home inspector noted the exposed copper grounds and the stripped ends on copper conductors were black or tarnished inside the panel ? First thought I had was chinese drywall issue but no other issues in the home . I we looked deeper the home is about 10-12 y.old and the only thing that was strange was if the soil outside may be leaching some sort of corrosive gas thru the underground feeder power riser to the meterbase ? The panel is back to back with it and the ground wire to the grounding rod was clean as it entered the bay below the meterbase but blackened once it was in the panel ? Has anyone ever experienced anything like this ? Thank you in advance for responses.

Work Gear for Electricians and the Trades
Re: Blackened bare copper in panel ? [Re: Lectricfishrman] #218820
10/25/17 04:13 PM
10/25/17 04:13 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
It is still probably sulfur in the air. The good news is it really seems pretty harmless in spite of all of the hysteria.


Greg Fretwell
Re: Blackened bare copper in panel ? [Re: Lectricfishrman] #218821
10/25/17 04:43 PM
10/25/17 04:43 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
It looks like Virginia did have some Chinese drywall problems and 2005 (12 years ago) would put that house in the right time frame

[Linked Image]

Here are some things I found when I was inspecting drywall problems here in Florida (ground zero for the problem)

http://gfretwell.com/ftp/Chinese%20Drywall/devices.html

The whole gallery is here (use your back button to exit each pictures)

http://gfretwell.com/ftp/Chinese%20Drywall/

Once the smell goes away and the sulfur dissipates it is very possible that they cleaned up all of the evidence and they may have actually replaced some or most of the drywall, so it is possible that you are looking at a drywall house and they just did not do anything about cleaning up the panel.
I would call it no big deal but as a buyer I still might want a break on the price unless they told me a really good story.
I do know a guy who was rehabilitating these houses but he went back to the FEPAC removing every bit of the drywall, sealing the block and started over. (new carpet, new cabinets, new plumbing fixtures, all devices were replaced etc)
That was probably more than was necessary but he wanted a clear conscience when he sold the house.


Greg Fretwell
Re: Blackened bare copper in panel ? [Re: Lectricfishrman] #218822
10/26/17 10:22 AM
10/26/17 10:22 AM
L
Lectricfishrman  Offline OP
New Member
Joined: Apr 2008
Posts: 6
Va.
Does anyone have a suggestion on how to remove the tarnish safely. Thank you your inputs.

Re: Blackened bare copper in panel ? [Re: Lectricfishrman] #218823
10/26/17 10:30 AM
10/26/17 10:30 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
If you have enough free conductor, cut off the exposed part, strip and re terminate.Other than esthetics, it is really not a problem. It does invoke thoughts of chinese drywall tho. On the bare grounds, steel wool will work, the finer grade the better.


Greg Fretwell
Re: Blackened bare copper in panel ? [Re: Lectricfishrman] #218831
10/29/17 11:18 AM
10/29/17 11:18 AM
Potseal  Offline
Member
Joined: Feb 2013
Posts: 264
Saskatchewan
Haven't seen it at the panel but I ran into it out in the field at receptacles and switches in one area of a hospital ward. If you pulled a receptacle out at the west or east end of the ward the copper was fine. But in between those two areas I found several where the copper was blackened. Assumed it was a reaction to cleaning chemicals used on equipment in that area.


A malfunction at the junction
--------------------------------------
Dwayne
Re: Blackened bare copper in panel ? [Re: Lectricfishrman] #218838
11/04/17 12:16 PM
11/04/17 12:16 PM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 947
Regina, Sask.
Hydrogen sulfide around oil processing equipment turns copper black over night. The solution was to use insulated ground wire and paint exposed terminations, like on ground rods, with glyptol.

Re: Blackened bare copper in panel ? [Re: Lectricfishrman] #218960
12/31/17 11:17 PM
12/31/17 11:17 PM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,250
SI,New Zealand
Are you sure this isn't moisture ingress?
Copper turns green (verdigris) then black with moisture exposure and can be a mode of conductor failure over time.
I use bootlace ferrules on all of my terminations these days, so that there is no real exposed copper.

Re: Blackened bare copper in panel ? [Re: Lectricfishrman] #219004
01/10/18 08:35 AM
01/10/18 08:35 AM
A
andey  Offline
Member
Joined: Aug 2008
Posts: 47
germany
There is another possible cause and that's a bad chemical mix in the PVC. I believe that mostly black PVC is affected.
Stripping these won't help, the copper is black on the full length.

Last edited by andey; 01/10/18 08:38 AM.

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,337 Are you busy
187,961 Re: Forum
177,501 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.031s Queries: 15 (0.005s) Memory: 1.0052 MB (Peak: 1.1758 MB) Zlib enabled. Server Time: 2018-10-17 16:17:43 UTC