1600 amp 480/277v 4 wire Y service #218826 10/28/17 11:51 AM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
Four Four inch from utility Transformer to CT Cabinet then to MCC. (XHHW).

three 600MCM & one 350 MCM each Conduit .

600 at 75C 420 amps x 4 = 1680 amp.

Very low Neutral load mostly 480 volt loads.

Using 310.15 (5) so no derating.

Engineer wants to use six six inch with four 400 mcm in each conduit.

I think conduit way over sized!

2017 / 2014 NEC & Related Books and Study Guides
Re: 1600 amp 480/277v 4 wire Y service [Re: Yoopersup] #218827 10/28/17 12:05 PM
Joined: Jul 2004
Posts: 9,383
G
gfretwell Offline
Member
Maybe he got hollered at for spec'ing to small a conduit before.
How long and how many bends?
Sometime what "fits" is not what you want to pull.
Your ampacity looks OK to me


Greg Fretwell
Re: 1600 amp 480/277v 4 wire Y service [Re: Yoopersup] #218828 10/28/17 01:17 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
transformer to ct cabinet 35 ft .
ct cabinet to mcc max 10 ft.
you figure.????

Re: 1600 amp 480/277v 4 wire Y service [Re: Yoopersup] #218829 10/28/17 09:05 PM
Joined: Jul 2004
Posts: 9,383
G
gfretwell Offline
Member
It might be interesting to ask the engineer what his thinking is on this project. He may have just decided nobody ever got in trouble going too big ... as long as it isn't his money. wink


Greg Fretwell
Re: 1600 amp 480/277v 4 wire Y service [Re: Yoopersup] #218830 10/28/17 10:28 PM
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
Maybe he will be paid a percentage of the job.

Re: 1600 amp 480/277v 4 wire Y service [Re: Yoopersup] #218832 10/30/17 12:53 AM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline
Member
Space for future expansion? Cost pennies now versus dollars later


"Live Awesome!" - Kevin Carosa
Re: 1600 amp 480/277v 4 wire Y service [Re: Yoopersup] #218833 10/30/17 11:33 AM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
Transformer 1000 KVA ( 1208 Amps ) Switch Gears 1600 amps .

Utility Co. Never sizes as per our calculations. I called them on it.

There reply no problem.

Re: 1600 amp 480/277v 4 wire Y service [Re: Yoopersup] #218835 11/02/17 03:52 PM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
That happens all the time.
Utilities always go much further into their overload ratings than we do.
I remember seeing (3) 2,500A Switchboards fed from a vault that (when I looked inside) only had a single transformer in it.


Ghost307
Re: 1600 amp 480/277v 4 wire Y service [Re: Yoopersup] #218836 11/02/17 11:21 PM
Joined: Jul 2004
Posts: 9,383
G
gfretwell Offline
Member
That is also pretty common in residential. They put a 50 KVA pole pig on 3 "all electric" homes with 200a panels. I understand most of the time they are still loafing along but there are times I am surprised that they are not smoking.
Take a cool Christmas eve, oven going, 2 or 3 burners going on the cook top every light in the house on plus outdoor lighting, hot water and 15kw heat strips going in the air handlers ... times 3


Greg Fretwell
Re: 1600 amp 480/277v 4 wire Y service [Re: Yoopersup] #218837 11/03/17 07:05 PM
Joined: Apr 2002
Posts: 7,105
HotLine1 Offline
Member
Hi guys
Been AWOL for a bit.
Our POCO does not allow any reduced neutrals; no way; all conductors must be full size.
They also 'may' have an issue with 6x6" conduits; next time I talk with my POCO inspector, I'll run it by.

I can't say I've seen anything larger than 4", except for HV


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
GeneSF 6
Popular Topics(Views)
257,984 Are you busy
193,707 Re: Forum
183,315 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3