0 members (), 483 guests, and 9 robots.
Y
2400 volt ungrounded customer owned feeder from OCP .
Run underground in PVC
, Equipment ground required ?? Shield as ground ???
2017 NEC Part X.
I'd prefer EGC. But I think Shield allowed in some cases.
Code section with answer Please.
If EGC required sized by 250.122.
Yoopersup
You would need to run an actual ground conductor.
The shield won't do the job.
Yes; size it per 250.122.
Although technically the NEC doesn't mandate that you ground the 2400V system; I have always run a ground conductor...even if later someone tells me to not connect it.
Ghost307
250.4(B) talks about grounding equipment on ungrounded systems. Although it does not specifically reference 250.122 it is implied as a good guideline with these words
250.4(2) Bonding of Electrical Equipment. Non–current-carrying conductive materials enclosing electrical conductors or equipment, or forming part of such equipment, shall be connected together and to the supply system grounded equipment in a manner that creates a low-impedance path for ground-fault current that is capable of carrying the maximum fault current likely to be imposed on it.