2400 volt ungrounded customer owned feeder from OCP .
Run underground in PVC

, Equipment ground required ?? Shield as ground ???

2017 NEC Part X.
I'd prefer EGC. But I think Shield allowed in some cases.
Code section with answer Please.

If EGC required sized by 250.122.

Yoopersup

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: May 2005
Posts: 984
Likes: 1
G
Member
You would need to run an actual ground conductor.
The shield won't do the job.
Yes; size it per 250.122.

Although technically the NEC doesn't mandate that you ground the 2400V system; I have always run a ground conductor...even if later someone tells me to not connect it.


Ghost307
Joined: Jul 2004
Posts: 9,791
Likes: 14
G
Member
250.4(B) talks about grounding equipment on ungrounded systems. Although it does not specifically reference 250.122 it is implied as a good guideline with these words

Quote
250.4(2) Bonding of Electrical Equipment. Non–current-carrying conductive materials enclosing electrical conductors or equipment, or forming part of such equipment, shall be connected together and to the supply system grounded equipment in a manner that creates a low-impedance path for ground-fault current that is capable of carrying the maximum fault current likely to be imposed on it.


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Top Posters(30 Days)
triple 2
Popular Topics(Views)
303,305 Are you busy
232,258 Re: Forum
217,016 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5