ungrounded 2400 volt feeders #218718 08/30/17 08:17 AM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
2400 volt ungrounded customer owned feeder from OCP .
Run underground in PVC

, Equipment ground required ?? Shield as ground ???

2017 NEC Part X.
I'd prefer EGC. But I think Shield allowed in some cases.
Code section with answer Please.

If EGC required sized by 250.122.

Yoopersup

2017 / 2014 NEC & Related Books and Study Guides
Re: ungrounded 2400 volt feeders [Re: Yoopersup] #218719 08/30/17 11:16 AM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
You would need to run an actual ground conductor.
The shield won't do the job.
Yes; size it per 250.122.

Although technically the NEC doesn't mandate that you ground the 2400V system; I have always run a ground conductor...even if later someone tells me to not connect it.


Ghost307
Re: ungrounded 2400 volt feeders [Re: Yoopersup] #218722 08/31/17 11:58 AM
Joined: Jul 2004
Posts: 9,555
G
gfretwell Offline
Member
250.4(B) talks about grounding equipment on ungrounded systems. Although it does not specifically reference 250.122 it is implied as a good guideline with these words

Quote
250.4(2) Bonding of Electrical Equipment. Non–current-carrying conductive materials enclosing electrical conductors or equipment, or forming part of such equipment, shall be connected together and to the supply system grounded equipment in a manner that creates a low-impedance path for ground-fault current that is capable of carrying the maximum fault current likely to be imposed on it.


Greg Fretwell

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 810
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 15
NORCAL 10
Popular Topics(Views)
273,971 Are you busy
207,724 Re: Forum
195,435 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3