ungrounded 2400 volt feeders #218718
08/30/17 09:17 AM
08/30/17 09:17 AM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 849
Michigan
2400 volt ungrounded customer owned feeder from OCP .
Run underground in PVC

, Equipment ground required ?? Shield as ground ???

2017 NEC Part X.
I'd prefer EGC. But I think Shield allowed in some cases.
Code section with answer Please.

If EGC required sized by 250.122.

Yoopersup

2017 / 2014 NEC & Related Books and Study Guides
Re: ungrounded 2400 volt feeders [Re: Yoopersup] #218719
08/30/17 12:16 PM
08/30/17 12:16 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 971
Chicago Illinois USA
You would need to run an actual ground conductor.
The shield won't do the job.
Yes; size it per 250.122.

Although technically the NEC doesn't mandate that you ground the 2400V system; I have always run a ground conductor...even if later someone tells me to not connect it.


Ghost307
Re: ungrounded 2400 volt feeders [Re: Yoopersup] #218722
08/31/17 12:58 PM
08/31/17 12:58 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,343
Estero,Fl,usa
250.4(B) talks about grounding equipment on ungrounded systems. Although it does not specifically reference 250.122 it is implied as a good guideline with these words

Quote
250.4(2) Bonding of Electrical Equipment. Non–current-carrying conductive materials enclosing electrical conductors or equipment, or forming part of such equipment, shall be connected together and to the supply system grounded equipment in a manner that creates a low-impedance path for ground-fault current that is capable of carrying the maximum fault current likely to be imposed on it.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Albert 3
Popular Topics(Views)
253,890 Are you busy
190,323 Re: Forum
180,038 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 15 (0.004s) Memory: 0.9516 MB (Peak: 1.0774 MB) Zlib enabled. Server Time: 2019-03-22 04:50:57 UTC