When is a Class 2 circuit, isn't?.... #217848
12/15/16 11:34 PM
12/15/16 11:34 PM
S
sparkyinak  Offline OP
Member
Joined: Jul 2007
Posts: 1,334
Alaska
For Ghits and Siggles....

If a Class 2 circuit is protected by an properly sized OCPD, is it really a Class 2 circuit or is it a Class 1 circuit and can be treated as a Class 1 circuit as long it meets the requirements of a Class 1 circuit as needed?

....and go!


"Live Awesome!" - Kevin Carosa
Work Gear for Electricians and the Trades
Re: When is a Class 2 circuit, isn't?.... [Re: sparkyinak] #217850
12/17/16 03:44 AM
12/17/16 03:44 AM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,227
Estero,Fl,usa
A class 2 is inherently protected by the limited current power supply so the only reason for OCP is protecting equipment.


Greg Fretwell
Re: When is a Class 2 circuit, isn't?.... [Re: sparkyinak] #217851
12/17/16 06:52 PM
12/17/16 06:52 PM
S
sparkyinak  Offline OP
Member
Joined: Jul 2007
Posts: 1,334
Alaska
I understand what a class 2 circuit is, hence the question. I'm not abvocating this but let's say one need to dim LED lights (0-10V) and there's no practical way to run a seperate raceway to the light. If one would properly fused the dimmer circuit and used appropriate voltage rated wire, could both the lighting circuit and dimmer circuit be in the same raceway?


"Live Awesome!" - Kevin Carosa
Re: When is a Class 2 circuit, isn't?.... [Re: sparkyinak] #217852
12/17/16 07:40 PM
12/17/16 07:40 PM
HotLine1  Online Content

Member
Joined: Apr 2002
Posts: 6,972
Brick, NJ USA
Based on your scenario...I see no problem.



John
Re: When is a Class 2 circuit, isn't?.... [Re: sparkyinak] #217853
12/18/16 02:01 AM
12/18/16 02:01 AM
Potseal  Offline
Member
Joined: Feb 2013
Posts: 264
Saskatchewan
I might be misunderstanding the scenario but if the light is 120V AC and the dimming is 0-10V DC and they are both in the same raceway running parallel over a long distance isn't there a possible issue of interference with the AC to the DC? Sparkyinak's scenario might be to code but ultimately it could lead to problems.


A malfunction at the junction
--------------------------------------
Dwayne
Re: When is a Class 2 circuit, isn't?.... [Re: Potseal] #217855
12/18/16 02:12 AM
12/18/16 02:12 AM
S
sparkyinak  Offline OP
Member
Joined: Jul 2007
Posts: 1,334
Alaska
Granted this is all hypothetical but with your theory has possible merit. In a situation like that, I'd use shielded cable for the signaling.


"Live Awesome!" - Kevin Carosa
Re: When is a Class 2 circuit, isn't?.... [Re: sparkyinak] #217856
12/18/16 05:06 AM
12/18/16 05:06 AM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,227
Estero,Fl,usa
I have questioned the Class 1 thing a few times and it is possible. You just need to follow all of the class 1 rules from end to end.

The chance of coupling harmful amounts of 60hz in any raceway that is not measured in miles is infinitesimal.
You are generally talking about 2 balanced conductors for each voltage. The twist necessary at 60hz is what you see on transmission lines.

If the raceway is actually a "duct" (referenced but undefined in the NEC) cable jackets can be the isolation although they usually have an additional isolating innerduct/raceway in there.

BTW along these lines, I have also heard the argument that a cable jacket is "isolation" so if you had a chapter 3 and a 725 cable in the same raceway, they are isolated. You just can't terminate them in the same box (generally).
The scenario was you have a raceway with a (say Romex) in it. You have "T" body conduit body at each end just before you enter the chapter 3 box. You come in the side with a low voltage cable and exit before you get to the box on the other end. Is that legal?

It is a conversation starter anyway.


Greg Fretwell
Re: When is a Class 2 circuit, isn't?.... [Re: sparkyinak] #217858
12/19/16 04:14 AM
12/19/16 04:14 AM
S
sparkyinak  Offline OP
Member
Joined: Jul 2007
Posts: 1,334
Alaska
I'd have to grab my code book from the office. Interesting question. My initial take is if the signal circuit is class 2 or 3 circuit, I'd say no


"Live Awesome!" - Kevin Carosa
Re: When is a Class 2 circuit, isn't?.... [Re: sparkyinak] #217859
12/19/16 11:58 AM
12/19/16 11:58 AM
HotLine1  Online Content

Member
Joined: Apr 2002
Posts: 6,972
Brick, NJ USA
Guys:

This months issue of EC Magazine has an ad for "Encore Wire" new MC-LED AL cable. Seems to solve any issues like this.

I have not read it thoroughly, but on a quick read seems OK

www.encorewire.com is the website in the ad.



John
Re: When is a Class 2 circuit, isn't?.... [Re: sparkyinak] #217860
12/19/16 07:34 PM
12/19/16 07:34 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,227
Estero,Fl,usa
Combo class 2/3 plus chapter 3 cables have been around for quite a while.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008