ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat Box
Recent Posts
FPE in Germany
by NORCAL - 10/16/19 08:24 AM
Help with aging employee advice.
by Bill Addiss - 10/15/19 10:58 PM
Fuse blower plug?
by gfretwell - 10/13/19 03:23 PM
Power factor and transformer efficiency
by TeslaEdison - 10/13/19 04:05 AM
Permit Snafus...AHJs and Contractors Jump in
by HotLine1 - 10/10/19 07:35 AM
New in the Gallery:
FPE Breaker panel in germany
What is this for?
Who's Online Now
1 registered members (Scott35), 11 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Temporarily feeding a panel... #217649 09/29/16 04:29 PM
Joined: Feb 2013
Posts: 264
Potseal Offline OP
Member
...from a second separately derived system.

For example, the panel is fed from a building substation that is designated for emergency power (backed up by an onsite generator). Now you wish to temporarily shut down the power upstream from that panel in order to perform work on the system. This particular panel feeds equipment that is essential to the building and needs to be kept powered-up during the shut-down. In the same location there is a panel that has the capacity to feed the panel for the essential equipment but it is fed from a second substation that feeds non-essential equipment. Since this other panel is fed from a separately derived system do you have to switch the neutrals when transferring?


A malfunction at the junction
--------------------------------------
Dwayne
Tools for Electricians:
Re: Temporarily feeding a panel... [Re: Potseal] #217650 09/29/16 06:23 PM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
IMHO...Yes.


Ghost307
Re: Temporarily feeding a panel... [Re: Potseal] #217651 09/29/16 08:10 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Not just 'yes,' but HELL YES.

Electricity wants / needs to go "home.' Home is where it is created. In most cases, this is the last transformer in the system, where the neutral was created.

Sending the neutral to another transformer is useless at best!

The ONLY place that neutral can terminate is at the same transformer that supplies the 'hots.'

Re: Temporarily feeding a panel... [Re: Potseal] #217652 09/29/16 10:07 PM
Joined: Apr 2002
Posts: 7,121
HotLine1 Offline
Member
Potseal:

As Ghost and Reno say...Yes! and Hell YES!!

Some bad things could happen by using the neutral of one SDS connected to another SDS neutral.


John
Re: Temporarily feeding a panel... [Re: Potseal] #217653 09/30/16 02:05 AM
Joined: Feb 2013
Posts: 264
Potseal Offline OP
Member
Thanks for the replies.

This question comes as a result of an actual project that I am involved in. I was asked by my supervisor to prepare to feed an Emergency power panel from a Normal power panel which will be part of a major electrical shutdown at the building where I work. When he stated that I only need to connect the hots I felt there was something wrong but decided I should do some research before discussing it with him. I looked in the CEC for a rule regarding this but found nothing. I then looked for articles online and read what I thought was related information. One article seemed to make it clear that a significant hazard would be compromising of any ground fault protection. As well, I contacted an electrical engineer whose projects I often work on. His main concern was backfeeding. Naturally I had to pose the question here. The results are unanimous and I can now approach him with confidence that we will need to switch the neutrals.


A malfunction at the junction
--------------------------------------
Dwayne

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
sparky 10
Popular Topics(Views)
259,527 Are you busy
194,919 Re: Forum
184,354 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3