ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
12 Lead Motor Connection Weird
by emolatur - 01/19/22 02:40 PM
Any women electricians here?
by gfretwell - 01/17/22 01:44 PM
Well There's your problem.
by gfretwell - 01/08/22 12:17 AM
Happy New Year!!
by HotLine1 - 01/04/22 09:50 AM
Sangamo s309.2
by Robski - 12/31/21 04:54 PM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 48 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Feb 2013
Posts: 264
Potseal Offline OP
Member
...from a second separately derived system.

For example, the panel is fed from a building substation that is designated for emergency power (backed up by an onsite generator). Now you wish to temporarily shut down the power upstream from that panel in order to perform work on the system. This particular panel feeds equipment that is essential to the building and needs to be kept powered-up during the shut-down. In the same location there is a panel that has the capacity to feed the panel for the essential equipment but it is fed from a second substation that feeds non-essential equipment. Since this other panel is fed from a separately derived system do you have to switch the neutrals when transferring?


A malfunction at the junction
--------------------------------------
Dwayne
Joined: May 2005
Posts: 984
Likes: 1
G
Member
IMHO...Yes.


Ghost307
Joined: Jan 2005
Posts: 5,316
Cat Servant
Member
Not just 'yes,' but HELL YES.

Electricity wants / needs to go "home.' Home is where it is created. In most cases, this is the last transformer in the system, where the neutral was created.

Sending the neutral to another transformer is useless at best!

The ONLY place that neutral can terminate is at the same transformer that supplies the 'hots.'

Joined: Apr 2002
Posts: 7,288
Likes: 4
Member
Potseal:

As Ghost and Reno say...Yes! and Hell YES!!

Some bad things could happen by using the neutral of one SDS connected to another SDS neutral.


John
Joined: Feb 2013
Posts: 264
Potseal Offline OP
Member
Thanks for the replies.

This question comes as a result of an actual project that I am involved in. I was asked by my supervisor to prepare to feed an Emergency power panel from a Normal power panel which will be part of a major electrical shutdown at the building where I work. When he stated that I only need to connect the hots I felt there was something wrong but decided I should do some research before discussing it with him. I looked in the CEC for a rule regarding this but found nothing. I then looked for articles online and read what I thought was related information. One article seemed to make it clear that a significant hazard would be compromising of any ground fault protection. As well, I contacted an electrical engineer whose projects I often work on. His main concern was backfeeding. Naturally I had to pose the question here. The results are unanimous and I can now approach him with confidence that we will need to switch the neutrals.


A malfunction at the junction
--------------------------------------
Dwayne

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Top Posters(30 Days)
Robski 1
Popular Topics(Views)
288,168 Are you busy
220,239 Re: Forum
206,230 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5