commercal service bonding two 200 amp services from a 400 amp meter with two sets of 3/0 cu to each panel no bonding allowed in meter can, do I tie both net together with a 1/0 cu from water pipe and a # 6 from ground rod and a #4 to each panel in the wireway and bond there or one #4 from the water pipe and one #6 from the rod to each panel.

Last edited by lite bulb; 08/21/16 08:17 PM.
Horizontal Ad
Joined: Jul 2004
Posts: 10,006
Likes: 37
G
Member
The easiest way would be to loop a GEC, based on the conductors feeding the panels (250.66) down from one to the water pipe, through the clamp and up to the other.
You can size to each panel. The other option is to run a GEC sized to the SE conductors (250.66) up towards the panels and splice the appropriate GEC from the panel to that.

From the handbook
[Linked Image from gfretwell.com]


Greg Fretwell
Joined: Jan 2005
Posts: 5,476
Likes: 3
Cat Servant
Member
I thought - and I'm begging for correction here- that:

A) No splices were allowed in the GEC; and,

B) You were never required (by NEC) to exceed #6 for the GEC.

Joined: Jul 2004
Posts: 10,006
Likes: 37
G
Member
You can't splice the GEC but you can splice a GEC "tap. Clear as mud huh?
That is why I said the easiest way is to loop one #4 or #2 through the pipe clamp and then you will not get a fight ... unless they actually want to size it to the SE conductors per 250.66

The GEC is limited to the rating of the electrode. A rod is #6, A Ufer #4 and a water pipe, the full size called for in 250.66


Greg Fretwell
Joined: Feb 2006
Posts: 78
L
Member
My question is can I tie the 3/0 net together in the wireway and do my bonding there dropping a #4 down to each panel

Joined: Apr 2002
Posts: 7,411
Likes: 8
Member
lite bulb:

"My question is can I tie the 3/0 net together in the wireway"

Do you mean to install 3/0 feeder into the wireway?? Or ??


John
Joined: Jan 2005
Posts: 5,476
Likes: 3
Cat Servant
Member
Great answer, Greg!

Another quibble I have with the artwork is that it appears to show a GEC that is larger than the service 'hot.'

Again, you're never required to have a BEC larger than the 'hot.'

I'm not sure you're required to have the GEC 'land' in every panel (or disconnect). As I see it, 1 meter = 1 GEC, land it in whichever panel is convenient.

No? I'm thinking of the meter bank at the apartment building across the street .... 12 meters, one GEC landing in one place.

Using Holt's explanation (ground rod for lightning / static only), I see the issue also as one grounding electrode for
each building. I don't see the pictured 'tap' as accomplishing anything at all.

XXXXXXXXXXXXXXXXX

As for lite bulb's second question ....

TWO sets of 3/0? A parallel feed? Well, that's a different way to do it ....

First, I'm uncomfortable feeding the panels without having a disconnect first.

I'd run 500's to a trough above the panels (as in the drawing), and tap off then with 3/0's for each panel (using NSI's).

Could you run your GEC taps up into that trough, splice them together and run the GEC from the trough to your electrodes? I don't see why not- assuming the trough remains accessible (not sealed by the PoCo).

Horizontal Ad
Joined: Jul 2004
Posts: 10,006
Likes: 37
G
Member
The easiest way is to land the full sized 250.66 GEC in the meter/CT can and be done with it. Some PoCos may not allow that but it is the preferred method here.
You use an RNC nipple to get through the wall to the service disconnect with 3 (or 4 for 3p) wires and hit the bus with the MBJ. That satisfies the inspectors who don't want a parallel neutral path although, on the line side of the MBJ, I am not sure that matters.

A agree as soon as NFPA allows "taps" the idea of an unspliced GEC flies out the window.


Greg Fretwell
Joined: Feb 2006
Posts: 78
L
Member
Whats the differance between this and residental when you run two 200amp service cables out of a meter one to each panel?

Joined: Feb 2006
Posts: 78
L
Member
power co. will not allow bonding in meter box and the water pipe is to far away 200' to loop the EGC to each panel just thought it would be faster cheaper to do it this way.

Page 1 of 2 1 2

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 240
Joined: March 2005
Top Posters(30 Days)
Popular Topics(Views)
352,457 Are you busy
276,131 Re: Forum
255,636 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5