OK, here the enclosure bond is made via the neutral lug(s) that are mechanically connected to the enclosure in a 'hot sequence' install.

In a 'cold sequence' install (disco or MOCP ahead of the CTs) the neutral 'floats' and a bond for the CT cabinet is required.

See 250.122


John
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Mar 2003
Posts: 849
Y
Member
from the ct cabinet to the ist main the Neutral is your bond,
also install a bonding strap or jumper from XO in CT cabinet to cabinet. (Usually supplied by manufacturer of Cabinet.
If not size a conductor using 250.66

Installing EGC would give you a parallel neutral as your also required to bond in MDP.

See Soares grounding book or goggle Soares info on net

http://iaeimagazine.org/magazine/1998/11/01/service-main-bonding-jumpers/

Last edited by Yoopersup; 06/26/16 02:51 PM.