grounding a ct cabinet #217341 06/21/16 10:31 PM
Joined: Feb 2006
Posts: 78
L
lite bulb Offline OP
Member
I have a 800 amp service can I put just one 3/0 in one of the conduits from the main panel to ground the ct cabinet

2017 / 2014 NEC & Related Books and Study Guides
Re: grounding a ct cabinet [Re: lite bulb] #217342 06/21/16 10:59 PM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
No.
A fully rated grounding conductor must be routed in each of the conduits for parallel conductors.


Ghost307
Re: grounding a ct cabinet [Re: lite bulb] #217343 06/21/16 11:19 PM
Joined: Feb 2006
Posts: 78
L
lite bulb Offline OP
Member
thanks thats a 3/0 in each conduit right?

Last edited by lite bulb; 06/21/16 11:22 PM.
Re: grounding a ct cabinet [Re: lite bulb] #217344 06/22/16 07:34 AM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
Copper or Aluminum?


Ghost307
Re: grounding a ct cabinet [Re: lite bulb] #217347 06/22/16 10:18 AM
Joined: Apr 2002
Posts: 7,109
HotLine1 Offline
Member
Are you installing the GECs to the bond the neutrals in the CT? Or are you providing a bonding conductor for the CT cabinet?

Our POCO does not allow GECs in the CT cabinet, just bonding bushings IF required. Hot sequence the neutral block is bonded to the cabinet; cold sequence the neutral must 'float'. Then, bonding bushings may be required, dependent on the wiring method.

But, you are in Delaware, and Ghost is in Chicago, and I'm in NJ & referring to PSE&G rules.



John
Re: grounding a ct cabinet [Re: lite bulb] #217348 06/22/16 10:56 AM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
If you're installing 2 sets of 500kcmil as Service conductors, you'll need to use NEC table 250-66 to size the ground conductor in each conduit.


Ghost307
Re: grounding a ct cabinet [Re: lite bulb] #217352 06/22/16 11:27 PM
Joined: Feb 2006
Posts: 78
L
lite bulb Offline OP
Member
Main service is comming into the ct cabinet in pvc, leaving the cabinet to a metal trough also pvc, out of the trough to the 800 amp main panel also pvc. I'll have to check on grounding the ct cabinet with the power company but I still need to ground the trough bonding will be done in main panel. Wire is 500 copper.

Last edited by lite bulb; 06/22/16 11:39 PM.
Re: grounding a ct cabinet [Re: lite bulb] #217355 06/23/16 09:57 PM
Joined: Feb 2006
Posts: 78
L
lite bulb Offline OP
Member
Power company does want a ground to the ct cabinet from main panel do I need a 3/0 in each conduit to the ct cabinet from the main panel or can I just put one 3/0 in one conduit also grounding the trough?

Last edited by lite bulb; 06/23/16 09:59 PM.
Re: grounding a ct cabinet [Re: lite bulb] #217358 06/24/16 04:51 PM
Joined: Apr 2002
Posts: 7,109
HotLine1 Offline
Member
The POCO wants a "ground" in your CT cabinet; do they want the enclosure 'bonded' or the neutrals and GECs bonded at the CT enclosure?

IMHO, the POCO is looking to have the CT 'bonded'.



John
Re: grounding a ct cabinet [Re: lite bulb] #217365 06/25/16 02:38 AM
Joined: Feb 2006
Posts: 78
L
lite bulb Offline OP
Member
The enclocure bonded

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 233
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 11
Popular Topics(Views)
258,518 Are you busy
194,118 Re: Forum
183,620 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3