Angle of Conduit Entering an Enclosure #217214 06/04/16 01:47 AM
Joined: Mar 2004
Posts: 947
T
twh Offline OP
Member
I can't find the rule about the angle at which a conduit can enter a box through a KO. Is there one? It might have something to do with the need for a ground bushing because too much angle lifts one side of the lock nut (and connector) off the surface of the box.

Tools for Electricians:
Re: Angle of Conduit Entering an Enclosure [Re: twh] #217216 06/04/16 12:56 PM
Joined: Apr 2002
Posts: 7,109
HotLine1 Offline
Member
Off the top of my head, I can't put a specific NEC Article on it, except 110.12 regarding mechanical execution of work.

However, this Article is basically unenforceable as it is 'subjective' as to "neat and workmanlike manner".

Your comment regarding the connector/locknut not being flush with the KO goes back to NEC Art 250 and a 'stretch' would be NEC Article 110.3 (B): re. mfg install instructions.




Last edited by HotLine1; 06/04/16 12:59 PM. Reason: add comment

John
Re: Angle of Conduit Entering an Enclosure [Re: twh] #217217 06/06/16 10:35 AM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
I'm not aware of anything beyond 'neat and workmanlike manner".


Ghost307
Re: Angle of Conduit Entering an Enclosure [Re: twh] #217218 06/06/16 11:52 AM
Joined: Mar 2004
Posts: 947
T
twh Offline OP
Member
I thought it was a Canadian code or in a provincial supplement.

Re: Angle of Conduit Entering an Enclosure [Re: twh] #217232 06/08/16 01:54 PM
Joined: Jul 2008
Posts: 98
B
brsele Offline
Member
Originally Posted by twh
I can't find the rule about the angle at which a conduit can enter a box through a KO. Is there one? It might have something to do with the need for a ground bushing because too much angle lifts one side of the lock nut (and connector) off the surface of the box.

12-1008 requires at least 3 complete threads.

I would think that you're limited to going straight in.
Any bends would be made outside of the box.

Re: Angle of Conduit Entering an Enclosure [Re: twh] #217270 06/11/16 06:53 PM
Joined: May 2003
Posts: 1,154
dougwells Offline
Member
I would really want to use a reducing washers but that really wont give you enough threads,#2/3 acwu i need to use a 3/4 throat wet connector into a meter base and I seem to feel more comfortable to use the reducing washers on the larger Ko;s on MB


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 233
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 11
Popular Topics(Views)
258,518 Are you busy
194,118 Re: Forum
183,620 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3