ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Furnace igniter leaking noise to stereo
by Haligan. 05/21/18 03:28 PM
480 Delta
by ghost307. 05/21/18 10:38 AM
turning down possible problem customer
by HotLine1. 05/21/18 07:53 AM
electircal ageing test on IPC
by HotLine1. 05/14/18 09:42 AM
What estimating software do you recommend?
by wattsittoyou. 05/14/18 06:28 AM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
0 registered members (), 26 guests, and 7 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
COMMERCIAL BUS TAP - ALLOWED OR NOT? #217096
05/02/16 04:32 PM
05/02/16 04:32 PM
G
GISdude  Offline OP
New Member
Joined: Jun 2009
Posts: 3
Sac, CA
Hi guys,
For some commercial customers installing a bus tap instead of potentially removing some sections and installing new sections would be a cost saver. However, the bus that is at the main that is being touched/drilled/re-lugged might not be NEC/UL compliant after the pull section integrity has been "compromised". Any feelings on this? It's starting to come up a lot and we're discussing if this might be against the AHJ.

ThX for any help

Work Gear for Electricians and the Trades
Re: COMMERCIAL BUS TAP - ALLOWED OR NOT? [Re: GISdude] #217097
05/02/16 07:49 PM
05/02/16 07:49 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,964
Brick, NJ USA
Please explain where you are going with this a little clearer.

Basically, any modifications can be considered to 'void' the NRTL listing. All depends on specifics.


John
Re: COMMERCIAL BUS TAP - ALLOWED OR NOT? [Re: GISdude] #217098
05/03/16 08:26 AM
05/03/16 08:26 AM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 943
Chicago Illinois USA
Agreed.
Whenever I have had the existing bus drilled out to land additional cables I have had to arrange (and pay) for the UL folks to make a trip to the field to revalidate the UL listing because the equipment had been changed from the way that it was originally tested.
I wasn't crazy about the added expense, but the insurance wouldn't have paid in the event of an incident because the equipment would have lost its UL listing otherwise.


Ghost307
Re: COMMERCIAL BUS TAP - ALLOWED OR NOT? [Re: GISdude] #217099
05/03/16 12:03 PM
05/03/16 12:03 PM
G
GISdude  Offline OP
New Member
Joined: Jun 2009
Posts: 3
Sac, CA
From what I've been reading, ghost307, it looks as though this is the only option. UL or NRTL is going to have to for a field visit to inspect and re-certify the bussing. I assume this is pretty expensive...

Re: COMMERCIAL BUS TAP - ALLOWED OR NOT? [Re: GISdude] #217100
05/03/16 06:36 PM
05/03/16 06:36 PM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 943
Chicago Illinois USA
In my experience UL doesn't work cheap; but they're usually well worth it.

You might want to give them a call and see if they will give you a ballpark price...I don't know if it's in the hundreds or the thousands these days.


Ghost307
Re: COMMERCIAL BUS TAP - ALLOWED OR NOT? [Re: GISdude] #217101
05/03/16 08:36 PM
05/03/16 08:36 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
What has happened to our trade?

Just a few years ago, this very forum had nice chats where we discussed the drilling & tapping of bussbars- among other things. I dare say that ours is a construction trade, where we fabricate things on a daily basis. The stuff we get at the parts house is only our raw materials - none would expect it to be the 'finished' product!

I know several folks here have cut, drilled, tapped, bent, cleaned, and otherwise altered bussbars. Many have also had parts fabricated to replace discontinued products.

I don't know the exact circumstances of the OP's situation, so I cannot offer a specific opinion as to where the proposed work is wise. By the time you get your masters' or contractors' license, you're supposed to have some idea as to your own limitations.

"Equipment not evaluated ...."

This is the biggest bit of folderol of all. NOTHING is evaluated as we use it. Period.

For example, I did a lightning system today. Neither the UL-listed wire nor the UL-listed ground rod were ever evaluated by UL for use with the UL-listed Cadweld system. Yet, Cadweld is used successfully millions of times each week.

(I'd say 'look it up,' but UL asserts ownership of their standards, and want you to buy them. Well, we can't have just anyone reading them now, can we? You'll just have to trust me on this one).

We've also seen the silly assertion by UL that male NPT threads are suitable for use with only "certain" NPT female threads. Go figure!

Re: COMMERCIAL BUS TAP - ALLOWED OR NOT? [Re: GISdude] #217103
05/03/16 10:00 PM
05/03/16 10:00 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,964
Brick, NJ USA
Reno:
Let me delve into this a little deeper.

I have had numerous situations where modifications, or repairs had to be performed on buss, both in switchgear, and distribution buss.

The ECs called in a fabricator who operates a UL approved shop to fabricate and/or install what had to be done. Yes, when it was completed a UL document was presented and a 'field label' was put on the equipment.

This one shop also makes custom switchgear, buss tap boxes, and POCO approved CT cabinets.

Yes, the cost is premium, but the results are 100% no issue. Overall it usually is cheaper then a "do-over".

Think about the litigious society we are all living in, and everyone having to 'watch their backs'; doing our jobs 'by the book' is the way to go.









John
Re: COMMERCIAL BUS TAP - ALLOWED OR NOT? [Re: GISdude] #217104
05/03/16 11:37 PM
05/03/16 11:37 PM
G
GISdude  Offline OP
New Member
Joined: Jun 2009
Posts: 3
Sac, CA
Ok guys, a lot of good feedback. The main concern here is having a customer that can't afford to spend another $25k on a new piece of equipment and having a POCO/AHJ being a little more flexible about being "by the book".

Thanks again, I'm prolly going to have to call UL and find some local guy.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,856 Are you busy
184,208 Re: Forum
173,450 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.030s Queries: 15 (0.005s) Memory: 0.9953 MB (Peak: 1.1607 MB) Zlib enabled. Server Time: 2018-05-21 22:14:38 UTC