Fire Alarm Question #216432 12/16/15 01:25 PM
Joined: Feb 2004
Posts: 74
C
CRM Offline OP
Member
Hi all, I have a question regarding the new fire alarm code, CAN/ULC-S524. It says the supply and return conductors of an addressable loop must be in separate raceways or cables. Does anybody know if you can run the signal conductors in one of these raceways or do you need a separate raceway? Thanks for any help.

Tools for Electricians:
Re: Fire Alarm Question [Re: CRM] #216433 12/16/15 04:01 PM
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
I don't see anything about that in that standard nor in our code book.

Check with the company that will be doing the verification. Maybe ask the question in an email so the answer is in writing.

Re: Fire Alarm Question [Re: CRM] #216434 12/16/15 06:41 PM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
Down here in the lower half of the continent the concern is just that the entire system could be compromised if the single raceway is damaged; thus the requirement for a separate raceway.
I've never heard of an issue regarding the signal wiring; just the backbone of the system.

twh is right; an emailed question is probably the best way to handle it.


Ghost307

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 18
NORCAL 10
Popular Topics(Views)
274,325 Are you busy
208,178 Re: Forum
195,756 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3