680.22(B)(1) and post lamps #215719 07/07/15 10:37 AM
Joined: Mar 2004
Posts: 782
B
BigB Offline OP
Member
For the purposes of 680.22(B)(1) is the post considered as part of the luminaire? (2011 NEC)

Last edited by BigB; 07/07/15 10:37 AM.
2017 / 2014 NEC & Related Books and Study Guides
Re: 680.22(B)(1) and post lamps [Re: BigB] #215721 07/07/15 10:59 AM
Joined: Apr 2002
Posts: 7,238
HotLine1 Online Content
Member
IMHO, the 'post' is the support for the luminaire. The post height must place the luminaire at 12' above water.

The few that I have come upon used fiberglass/composite poles at 14', and on GFI circuit.

You should check with your local AHJ for his opinion.


John
Re: 680.22(B)(1) and post lamps [Re: BigB] #215723 07/07/15 01:13 PM
Joined: Jul 2004
Posts: 9,577
G
gfretwell Offline
Member
I agree with John on this. The post is just a support for the luminaire. If it is metal it needs to be part of the bonding grid too.


Greg Fretwell
Re: 680.22(B)(1) and post lamps [Re: BigB] #215726 07/07/15 02:28 PM
Joined: Apr 2002
Posts: 7,238
HotLine1 Online Content
Member
Thanks Greg, I omitted the bonding on metallic posts.

Squeezing in posts between hectic times in the office.


John
Re: 680.22(B)(1) and post lamps [Re: BigB] #215742 07/12/15 02:06 AM
Joined: Mar 2004
Posts: 782
B
BigB Offline OP
Member
We ended up moving one the lights. The original plans showed that we would have had over 5 feet but when the pool got dug and laid out somehow there was a foot missing, not our fault. They are post lamps mounted on top of a retaining wall so moving one was a lot of fun carving up the concrete blocks.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
akmaster
akmaster
alaska
Posts: 74
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 11
BigB 1
Popular Topics(Views)
277,947 Are you busy
211,408 Re: Forum
198,463 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3