#215719 07/07/15 09:37 AM
Joined: Mar 2004
Posts: 829
B
BigB Offline OP
Member
For the purposes of 680.22(B)(1) is the post considered as part of the luminaire? (2011 NEC)

Last edited by BigB; 07/07/15 09:37 AM.
Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
IMHO, the 'post' is the support for the luminaire. The post height must place the luminaire at 12' above water.

The few that I have come upon used fiberglass/composite poles at 14', and on GFI circuit.

You should check with your local AHJ for his opinion.


John
Joined: Jul 2004
Posts: 10,036
Likes: 37
G
Member
I agree with John on this. The post is just a support for the luminaire. If it is metal it needs to be part of the bonding grid too.


Greg Fretwell
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
Thanks Greg, I omitted the bonding on metallic posts.

Squeezing in posts between hectic times in the office.


John
Joined: Mar 2004
Posts: 829
B
BigB Offline OP
Member
We ended up moving one the lights. The original plans showed that we would have had over 5 feet but when the pool got dug and laid out somehow there was a foot missing, not our fault. They are post lamps mounted on top of a retaining wall so moving one was a lot of fun carving up the concrete blocks.