#21563 02/05/03 02:02 PM
Joined: Nov 2001
Posts: 23
R
rayh78 Offline OP
Member
Installed a 100 watt mercury vapor outdoor light. It was fine until winter now its going thru bulbs. Problem started when customer is using a small electric space 1500watt heater on inside on same circut.
Is it a defective fixture or to much on circut.
Thanks

Joined: Apr 2001
Posts: 507
G
Member
What voltage do you have at the light with both the heater and light drawing current??

GJ

Joined: Nov 2001
Posts: 23
R
rayh78 Offline OP
Member
did not check, assumed if it was drawing to much would trip breaker

Joined: Jun 2001
Posts: 642
N
Member
The 100 watt light draws about.9 amp (100W/110V=.9091A)
The 1500 watt space heater draws (1500w/110v=13.6364A)
total draw is 14.5455A
A 20 Amp breaker will carry this all day.
A 15 amp breaker will propally carry this if the heater does not run all the time.
If 14AWG wire was used and the heater and light are over50-75' away you propably have a voltage drop causing the light to pull more than normal. If so the bulb will heat up more than normal and burn out much to soon.
You need to do a voltage check at the circuit breaker feeding this circuit and at the heater and at the light. Be careful and use a good quality meter. Avoltage drop of greater than 5% is a problem.
You may need to seperate the heater and light. Also check if anything else is on the circuit.
Good luck


ed
Joined: Jul 2002
Posts: 8,443
Likes: 3
Member
Ray,
One thing I do know, is that any type of Gas
Discharge lighting, does not particularly like Voltage drop, it can damage the control gear as well as the lamps.
If possible, I would put the MV Lighting on a dedicated circuit.