When derating THWN-2 copper conductors for ambient that will eventually terminate in a sub panel with a 125 amp rating can I use the 90C column?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jun 2004
Posts: 1,273
T
Member
The sole and only reason for that column IS derating.

For there are no 90 degree rated devices out there.

One then uses the lesser computed ampacity limit.

So, yes, you start with the 90 degree column.