Hi all,

I'm wondering if Square D Type QO Breakers come in tandem form (skinny taking up 1 slot only) for 30 & 40A. I can't seem to find them. I do find tandems in 15 & 20A though.

Reason : Installing arc-fault in a panel filled with all tandems (15/20), there is no more room. There are 3 double pole breakers each which take up 2 spaces. They are 40, 40, 30A.

So I'm not adding additional circuits, just arc-faults don't come in tandem. I'm trying to replace a 40, 40 or 30 with a skinny tandem and free up some room...otherwise replace panel.

Much appreciated.

Joined: Dec 2014
Posts: 4
New Member
Forgot to mention, I'm only installing 1 arc-fault breaker, which is creating this space issue.

Joined: Jul 2004
Posts: 9,677
Likes: 9
G
Member
I have never seen them over 20a. You are going to end up with a panel change or a sub panel IMHO.


Greg Fretwell
Joined: Apr 2002
Posts: 7,288
Likes: 4
Member
That's not something that I have seen. You may want to check Schneider website; or contact a local supply house that is a Sq D distributor. Not a 'big box' store, but a supply house.



John
Joined: Dec 2000
Posts: 4,289
Member
Double pole breakers can't replaced by tandems.

The double poles pick up both legs.
Tandems don't.

2 of them side by side won't be any help either. Handle ties won't fix the issue of the common trip requirement.


Joined: Mar 2004
Posts: 785
B
Member
You might have to install one of these next to the panel

http://www.leviton.com/OA_HTML/SectionDisplay.jsp?section=62350&minisite=10251


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 811
Joined: April 2004
Top Posters(30 Days)
NORCAL 3
grich 1
Popular Topics(Views)
287,879 Are you busy
220,049 Re: Forum
206,042 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5