Conduit penetration in top 3R Enclosure #214394 11/25/14 10:05 PM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline OP
Member
Hey fellow Sparkinators,

Thoughts any why:

PVC conduit penetration in top of 3R gutter with oil ring lock nut inside. Meet code?


"Live Awesome!" - Kevin Carosa
Work Gear for Electricians and the Trades
Re: Conduit penetration in top 3R Enclosure [Re: sparkyinak] #214395 11/26/14 03:05 AM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
A Myers hub with a T/A is going to pass...

Improvisations are entirely subjective -- as one has to depend upon the AHJ seeing things your way.

Your description is unclear. Do you mean the oil ring is on the outside of the NEMA3R gutter with the lock nut inside?

I've seen silicone used instead of an oil ring. I never new if that was inspected work or not.

In cold weather PVC contracts and becomes quite brittle. Throw in ice heave/ stress, and it's not a material that I'd favor in snow country.

More generally, it's a poor time-value descision to try and super-value-engineer assemblies -- particularly any assembly that is fully exposed to the elements. You stand at serious risk of getting shot down by the AHJ -- or by your one-year warranty obligation.

Your best time-value return comes from being very efficient and above all, not stumbling over materials/ materials shortages. The amount of time/ labor wasted because of materials shortages/ materials hard-to-find is leagues beyond any clever assembly scheme.

As for style points: anything that is highly visible to owners/ customers/ GCs should be assembled to look professional and handsome. Such work becomes a sales aid forever afterward.



Tesla
Re: Conduit penetration in top 3R Enclosure [Re: sparkyinak] #214396 11/26/14 03:59 AM
Joined: Jul 2004
Posts: 9,382
G
gfretwell Offline
Member
This is really more of a listing question than a code question. You could ask the installer to show you where that connector was listed as being rain tight.
If it was one of the male adapters like you get on a liquid tight assembly with the O ring, it may be.
I believe the installation instructions show the O ring goes on the outside between the shoulder of the adapter and the can.


Greg Fretwell
Re: Conduit penetration in top 3R Enclosure [Re: sparkyinak] #214397 11/26/14 04:46 PM
Joined: Apr 2002
Posts: 7,105
HotLine1 Offline
Member
There were locknuts that were supposed to be 3R, as they had a type of gasket on the shoulder. IF I remember correctly, the listing required one on each side (in & exterior).

I have not seen anyone use these in quite a while. IMHO, they were more of a pain (failure to prevent H2O entry). Myers hubs are the norm here.



John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
GeneSF 8
Popular Topics(Views)
257,879 Are you busy
193,608 Re: Forum
183,234 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3