Attachment point for residential service
#214218
10/30/14 01:46 AM
|
Joined: Mar 2006
Posts: 81
OP
Member
|
Why do they sell these? Can you use one of the knobs with the lag screw on the back or as I interpret the code, a long bolt through structural wood with a nut/washer on the back.
Incoming overhead cable is about 40ft. 6-112(6) says bolted but is a lag screw considered a bolt?
Im upgrading a 100A to 200A and don't want to rip the wall open unless absolutely necessary. I know the lag type insulator would hold but if they are not allowed by code, why do all the suppliers have lots on the shelves?
|
|
|
Re: Attachment point for residential service
[Re: bigpapa]
#214219
10/30/14 02:08 AM
|
Joined: Jun 2004
Posts: 1,273
Member
|
They are traditional for overhead runs between house and barn... and much else... on the customer's side of the meter.
The NEC does not cover Poco rules.
And the Poco rules dictate everything from the Service back up the line towards their distribution drop.
Locations Hardware Conductors Clearances
This is one area where a j-man has to make both inspectors happy. (County inspector & Poco inspector)
Out my way, the Pocos reject all manner of gear that qualifies by the standards of the NEC. (EUSERC)
Tesla
|
|
|
Re: Attachment point for residential service
[Re: bigpapa]
#214220
10/30/14 02:24 AM
|
Joined: Mar 2006
Posts: 81
OP
Member
|
Anybody here from BC Canada? Guess I will call the BCSA inspector about this.
|
|
|
Re: Attachment point for residential service
[Re: bigpapa]
#214223
10/30/14 03:27 PM
|
Joined: May 2003
Posts: 1,155
Member
|
For a 200 amp service, you will need the bolt through, At one time our inspector said that if the service was 100 amps and a short run to the pole they would accept the screw in type.
|
|
|
Re: Attachment point for residential service
[Re: bigpapa]
#214224
10/30/14 06:33 PM
|
Joined: Jul 2008
Posts: 98
Member
|
So in BC, do you really have to rip open the wall in a house when doing a 100A to 200A upgrade? (Obviously we're only talking about houses with an overhead service supply.)
I'm just curious.
|
|
|
Re: Attachment point for residential service
[Re: bigpapa]
#214225
10/30/14 10:10 PM
|
Joined: May 2003
Posts: 1,155
Member
|
Yes external masts have to be a bolt through securing method . attached in 3 places and the most highest clamp secured to a rafter
|
|
|
Re: Attachment point for residential service
[Re: bigpapa]
#214241
11/01/14 02:41 AM
|
Joined: Mar 2006
Posts: 81
OP
Member
|
I talked to the inspector this morning and he confirmed that bolted through is all that is accepted for 100A or 200A incoming cable attachment point.
|
|
|
|
|