Water tank de-icer - panel is 500-600' from tank #214048 09/26/14 02:21 AM
Joined: Feb 2013
Posts: 264
Potseal Offline OP
Member
I was asked today about the requirements for powering a 1500W 120V livestock water tank de-icer that was 500-600ft away from the panel. First thought that came to mind was "sub-panel". At that distance is it even reasonable to run conductors straight to the heater? At 500' and using a 3% voltage drop I ended up with #4 Cu (75 degree Celcius column Table 2 CEC). Wouldn't a small sub-panel placed closer to the tank and then running smaller gauge conductors to the heater be a better idea?


A malfunction at the junction
--------------------------------------
Dwayne
Tools for Electricians:
Re: Water tank de-icer - panel is 500-600' from tank [Re: Potseal] #214051 09/26/14 09:44 AM
Joined: Apr 2002
Posts: 7,258
HotLine1 Offline
Member
Potseal:

Vd for the load in the subpanel would be equal to what you calc'd for just the load.

IF you ran 3 wire & grd to the sub, you would have available 'load' capacity at the area.

Depending on available voltages at a source, 480 volt to the location, and a small 480-120 transformer may be economical.



John
Re: Water tank de-icer - panel is 500-600' from tank [Re: Potseal] #214053 09/26/14 01:52 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Potseal, you are under a misconception.

What limits voltage drop issues to branch conductors alone? Circuit or panel - you need to allow for voltage drop. Only a higher voltage will lessen your voltage drop.

Set the 'percentage rule' aside for the moment. What's your final voltage when the heater is in use? If your incoming voltage is on the high side (127V is not all that rare), then you could very easily have a very acceptable 118V at the heater.

Whether you should set a panel is another question. I'm biased in favor, for two reasons.
First, I like having an OCPD, GFCI, and disconnecting means close to the point of use.
Second, you almost always have a later desire to add a light, a service receptacle, whatever in the same area. Might as well pull a 4th wire and have a second circuit.

Run big pipe - pipe is cheap - and you can pull bigger wire later if you need it.

Finally ...don't have 480? Make it. Just use two transformers: one 'up' and one 'down.'

Re: Water tank de-icer - panel is 500-600' from tank [Re: Potseal] #214056 09/26/14 04:45 PM
Joined: Feb 2013
Posts: 264
Potseal Offline OP
Member
Thank-you for the suggestions. I will definitely consider them as it could solve the distance issue.

FYI

After doing my own calculations I decided to look online to see if I could compare my results to other available information. Found this related chart as a result:

[Linked Image from i61.tinypic.com]


A malfunction at the junction
--------------------------------------
Dwayne

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 19
Admin 8
Popular Topics(Views)
278,868 Are you busy
212,027 Re: Forum
199,064 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3