4800v. Directional Boring #213917 09/06/14 10:35 PM
Joined: Jan 2004
Posts: 1,498
G
George Little Offline OP
Member
Here's the deal (Ernie pay attention) can a contractor install a 4800v. feeder using directional boring run 1000 feet and not install a "Warning ribbon" 12" above the conductors? See (NEC 300.50).

Second question, if he needs the "warning ribbon" how does he install it?

Note- this is a feeder not Service conductors.


George Little
2017 / 2014 NEC & Related Books and Study Guides
Re: 4800v. Directional Boring [Re: George Little] #213918 09/07/14 02:27 PM
Joined: Apr 2002
Posts: 7,122
HotLine1 Offline
Member
George:
The only reference to 'directional boring' that I can find within the '11 NEC is 300.5 (k).

Neither relates directly toyour question.

Boring is something I have not come upon here.

There is no reference within 'over 600 volts' regarding boring that I find.

All the high voltage I come upon is in duct banks & concrete encased.


John
Re: 4800v. Directional Boring [Re: George Little] #213922 09/07/14 08:54 PM
Joined: Jan 2004
Posts: 1,498
G
George Little Offline OP
Member
Maybe the question should be: Can you directional bore customer owned conductors over 600v.


George Little
Re: 4800v. Directional Boring [Re: George Little] #213923 09/08/14 03:05 AM
Joined: Jul 2004
Posts: 9,412
G
gfretwell Offline
Member
I don't know about customer owed but the utilities do it all the time around here and I am sure they are not boring another hole for a warning ribbon.
They bored a HV line behind my house that I am betting was over 100kv. The existing on the poles is (2)48kv and 250kv.


Greg Fretwell
Re: 4800v. Directional Boring [Re: George Little] #213924 09/08/14 11:21 AM
Joined: Feb 2003
Posts: 350
M
mbhydro Offline
Member
Would boring in the orange HPDE pipe and then pulling the cable in be more acceptable?

Re: 4800v. Directional Boring [Re: George Little] #213929 09/08/14 09:36 PM
Joined: Apr 2002
Posts: 7,122
HotLine1 Offline
Member
George:
Talking to two HV guys today, neither has done any directional boring installs.

I'm curious to see if Scott35 has any comments from the 'shaky side'!!

Last two, and one upcoming (13.2KV) at the college are duct banks (4x5" PVC) and concrete encasement. (Red concrete), per specs.


John
Re: 4800v. Directional Boring [Re: George Little] #213941 09/10/14 09:42 AM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
George
Done all the time. Why DB if your gonna dig up the street or sidewalk to put ribbon.
Yoopersup

If we install HDPE in a open trench (which we do sometimes),
Ribbon is installed then.

Last edited by Yoopersup; 09/10/14 09:44 AM. Reason: Add
Re: 4800v. Directional Boring [Re: George Little] #213942 09/10/14 10:07 AM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline
Member
George
Conductors marked with a rated temperature higher than that of the raceway can be used when the conductors are operated within the raceway temperature rating.

One application of 353.10(6) is the use of 105C-rated medium voltage cables, Type MV, where the cable ampacity at
the 105C rating is reduced to the cable ampacity at 75C or 90C to match the listed operating temperature rating of HDPE (75C or 90C).
Direct bury power cable systems are designed for long life, use of HDPE conduit to encase and protect the power cable from rock impingement is gaining favor as it allows for quick and easy repairs without excavation of the cable. HDPE conduit and innerduct is used to carry low 600V-transformer to end user) and medium (<69kV-substation to transformer) voltage power lines.

Yoopersup

Re: 4800v. Directional Boring [Re: George Little] #213948 09/10/14 11:31 PM
Joined: Jan 2004
Posts: 1,498
G
George Little Offline OP
Member
Thanks Ernie, I knew you dealt with this type of installation on a regular basis and would have a good answer.

See ya in Frankenmuth.


George Little

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,281
Joined: December 2000
Show All Member Profiles 
Top Posters(30 Days)
BigB 5
Popular Topics(Views)
260,718 Are you busy
195,752 Re: Forum
185,139 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3