243
19
Posts: 7,413 Likes: 9
Opinions please gentlemen:
Can a fused pullout disconnect be converted to a non-fused disconnect??
ie: replace the fuses with 1/2" copper pipe.
I'm interested in opinions from any and all of you guys.
Posts: 10,035 Likes: 37
Electrically I suppose it is fine assuming you have overcurrent protection somewhere else.
How do you feel about "approving" unlisted products? (110.2)
Posts: 2,724 Likes: 1
Broom Pusher and Member
The "Dummy Fuses" referenced in Electure's posted Hyperlink, are useful in 3 Pole Safety Switches; where the System used is a 3 Phase 3 Wire Corner Grounded Delta.
This effectively opens all 3 Conductors (both Ungrounded Conductors and the Grounded Conductor) simultaneously, and keeps the Grounded Conductor "Solid" (No OCPD in Series) at the Disconnect / Safety Switch.
Footnote: When such an item is seen by "4 Wire Wye-Guys only", the reactions by those unfamiliar with Corner Grounded Systems range from a simple "Whaddaheck???" to "Evacuate The Building!!!"
After which comes the difficulty of trying to explain why the Identified (i.e. Grounded) Conductor is One of the Three Wires for this 3 Phase 3 Wire Branch Circuit - and why White or Gray Insulation / Tape on this Conductor is Code Compliant...
Most grasp the concept and accept the System's "Differences", while only a few (be they obnoxious, arrogant, or simply from Mule-Level Reluctance), refuse to accept any part of such an Alien System's use, operation and Code Compliance. (Note: I mention the latter, due to a few ugly debates from past installations...)
--Scott (EE)
The corner grounded systems I saw, (all sewer lift pumps) used equipment like single phase with two ungrounded conductors in a 2 pole breaker and a white grounded conductor with no overcurrent protection or disconnecting means at all. If there was a switch type disconnect, it was 2 pole. I admit, the first one I saw, standing there all alone with no help around had me pretty confused for a minute I am glad I had heard of corner delta and was glad I figured it out before I said something dumb.
Greg: Yes, there was OCP back at the breaker panel, amperage conforming to the mfg nameplate. (HVAC-CU)
The old disco is marked 'fuses within pullout'. This is on an engraved plate on the disco.
I know electrically it works, however IMHO copper pipe is not a fuse.
The installer left a message that he is looking for a 'solid' pullout. I thought good luck; the disco is 60s vintage. I think two 30 amp, 250 volt, TD fuses will be a lot cheaper and easier to find?
Electure: Thanks for the link.
Like I said it is only OK if you approve unlisted fuse replacements. I agree with you. Bussman makes one so they should be using that. (or just put in some real fuses)
HCE727
Delaware County, PA, USA