Outdoor transformer Customer owned 13.8 Pri.
480/277 Secondary. Bond at Transformer as Required 250.30 (C)
sized by 250.66. 3 phases from Transformer Plus Ground to ist OCP. Can it be Bare Conductors (Parallel) & Must be sized by 250.66 as it's before OCP.
250.30 (B) 3.
Phase Conductors 6 sets of 750's .
750 x6 = 4500 x 12.5 % =5625.
Grounding conductor must be 600 mcm each conduit.
Your imput ?

2017 / 2014 NEC & Related Books and Study Guides
Joined: Mar 2003
Posts: 849
Y
Member
Questions are incase I didn't state them correctly?
Can a bare SSBJ be installed between the XO at the secondary of the transformer to the Switchgear with the phase conductors?? (there is no Neutral just 3 phases & SSBJ.

Second: system bonding jumper must be sized by 250.66????

Yoopers UP
see above post for details



Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
timmp
timmp
Leo, IN, USA
Posts: 27
Joined: June 2004
Top Posters(30 Days)
timmp 3
Popular Topics(Views)
283,076 Are you busy
216,813 Re: Forum
203,189 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5