multicircuit breaker #212978 03/04/14 04:08 PM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
Does the rule on putting the breaker on breaker with tie handle pertain to commercial 3 phase? Thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: multicircuit breaker [Re: sparkync] #212979 03/04/14 07:50 PM
Joined: Apr 2002
Posts: 7,225
HotLine1 Offline
Member
From 2011 NEC:
Article 240
"(3) 3-Phase and 2-Phase Systems. For line-to-line loads
in 4-wire, 3-phase systems or 5-wire, 2-phase systems, individual single-pole circuit breakers rated 120/240 volts ac with identified handle ties shall be permitted as the protection for each ungrounded conductor, if the systems have a grounded neutral point and the voltage to ground does not exceed 120 volts."

There are other mentions within '11 I turned up via a search thru the PDF version. Most of them are specific to an installation. (DC; Bulk storage, etc)


John
Re: multicircuit breaker [Re: sparkync] #212983 03/04/14 09:05 PM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
On the job I'm working on, I think separate neutrals may be better. Circuits are coming out of an "ancient" 3 phase panel. A (3) phase breaker if it could be found, would cost a bundle. The junction boxes are not too far away. I was trying to conserve space in the conduit but the extra wire will be a lot cheaper. Thanks..

Re: multicircuit breaker [Re: sparkync] #212986 03/04/14 09:49 PM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
There is quite a community of second-hand breaker dealers.

You would be astounded as to how many ancient 3-phase breakers are available -- reconditioned -- off the shelf.

You can do an eBay search, a Web search, or hook up with known players in the marketplace.

Salinger (Michigan) immediately comes to mind. There are three outfits within 120 miles of my shop that deal in 2nd hand breakers, odd fuses, etc.

http://www.salingerelectric.com/

So, before you knock yourself out, pick up a phone. You might find that you can negotiate your price. It's not as if this stuff just jumps off the shelf.

Lastly, if you come across decent gear that is being replaced, these are the folks that buy such gear. It beats throwing the stuff away. The chance that a small EC is going to find a home for such gear is nil.


Last edited by Tesla; 03/04/14 09:51 PM.

Tesla
Re: multicircuit breaker [Re: sparkync] #212987 03/05/14 08:27 AM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
Forgot to mention above that these circuits are for florescent lighting only . I'm looking at an old 2005 code and it's referring saying if they " are on the same yoke"(outlet). ( don't have my 2011 with me now.

Last edited by sparkync; 03/05/14 08:29 AM.
Re: multicircuit breaker [Re: sparkync] #212988 03/05/14 09:28 AM
Joined: Apr 2002
Posts: 7,225
HotLine1 Offline
Member
sparkync:
This is from '08 NEC Check the FPN

"210.4 Multiwire Branch Circuits.
(A) General. Branch circuits recognized by this article shall be permitted as multiwire circuits. A multiwire circuit shall be permitted to be considered as multiple circuits. All conductors of a multiwire branch circuit shall originate from the same panelboard or similar distribution equipment.
FPN: A 3-phase, 4-wire, wye-connected power system used to supply power to nonlinear loads may necessitate that the power system design allow for the possibility of high harmonic currents on the neutral conductor.
(B) Disconnecting Means. Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates."


John
Re: multicircuit breaker [Re: sparkync] #213003 03/06/14 05:47 PM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member

Thanks John. I thought I remembered it was a good thing on florescent lights to have a separate neutral anyway.

Re: multicircuit breaker [Re: sparkync] #213005 03/06/14 08:43 PM
Joined: Apr 2002
Posts: 7,225
HotLine1 Offline
Member
You're welcome.
That's what we are all here for!


John
Re: multicircuit breaker [Re: sparkync] #213006 03/06/14 09:27 PM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
The PRIMARY reason why dedicated neutrals make so much sense is because of what happens during maintenance of the system.

To safely work on a circuit, every hot that's mated to its neutral has to be shut off, too.

In a 480Y277 system (ultra-common) that's a very big foot-print of dark territory. This is especially true for high-bays in a warehouse.

In contrast, it's as common as dust for grocery stores to use 3-hots (A,B,C) on ONE (oversized?) neutral for strip fluorescents. It's not so bad if a single row of lamps goes dark. BTW, these circuits are never loaded more than 10-11 amps on a 20 amp breaker at 277VAC to ground.

Hence, they're half-way to an oversized neutral via design restraint.

&&&

For those who've never wired large structures:

Voltage drop is a serious issue. CWA driven lamps will fail to fire up should you be so foolish as to wire up a circuit up towards NEC minimums. Such 'site lighting' runs must use 208VAC or better... only loading the conductors rather lightly. Any attempt to break this iron law will have you out -- time and again -- coming back on warranty calls as the fixtures misbehave.

Like motor loads, CWA's pull heavy to start. Their constant wattages mean extra heavy amps when the voltage drops. This can make them 'self-snuffing.' (The only solution is more wire.) This was alluded to in a prior post INRE EM fixtures.

Last edited by Tesla; 03/06/14 09:29 PM.

Tesla
Re: multicircuit breaker [Re: sparkync] #213013 03/07/14 09:42 AM
Joined: Apr 2002
Posts: 7,225
HotLine1 Offline
Member
Tesla:
I know a few DB guys that had some serious voltage drop issues. Both site lighting, and large bldgs.

Some guys learn the really hard way the first time.

Remote head E-lites used to be the big problem back when they were popular.



John
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 15
NORCAL 10
Popular Topics(Views)
273,990 Are you busy
207,749 Re: Forum
195,455 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3