1 members (Scott35), 455 guests, and 8 robots.
#212657 01/30/14 01:00 PM
cgw Offline OP
For a conduit installed for data cable (e.g. conduit from wall box up to above ceiling) - What should the minimum radius of the elbow be?
4 times the diameter of the cable is the min, for regular bends 50mm is the min.
Radius in such situations is almost never an issue.
The crippler is the size of the conduit.
Typical minimum for trivial need: 3/4"
Robust data-com spec out 1 1/4" drops -- for which j-boxes are in mass production (yet special order from your distributor -- such big KOs have to be spec'd) (4-11s)
It's not uncommon for the drops to have no elbow at all. Instead, the drop is a sleeve capped by a plastic bushing -- typically a white nylon style -- Arlington pitches theirs all the time in EC Magazine.
It's common for the spec's to call out for bushed entries, BTW. Bare pipe won't do.
Eriksen sells a bender that kicks out mild sweeps in EMT.
It's popular in the data-com world, too.
http://www.ericksenbender.net/
This is usually a company tool. Its sweeps are so gentle that it's possible to go to down a size for data-com sweeps. (ie, 1" replaces 1 1/4") If you do this often enough, then the bender pays for itself.
[ Note: downsizing data-com drops is only possible if you've got the data-com contract. In all other cases, you're in the blind -- and will have to follow the contract spec's. These are usually worked up on the most conservative (oversized) basis so that the writer doesn't get bit by final results.]
In all cases, never attempt to get away with 1/2" EMT.
Tesla
