Service disco/overcurrent devices in bathrooms #212428 01/06/14 06:14 PM
Joined: Feb 2001
Posts: 308
S
Steve T Offline OP
Member
I did a search and couldn't locate this topic--I'm pretty sure it's been discussed before. Pointers to an existing thread is great if someone has it. Otherwise--

1) What was the purpose/substantiation for not having a service disco in a bathroom?

2) Does anything prohibit passing 'through' a bathroom to gain access to the service disco?

3) (Lets get real silly)--Can the working clearance for the service disco be in the bathroom, while the service disco itself is actually out of the bathroom? e.g. closet door.

2017 / 2014 NEC & Related Books and Study Guides
Re: Service disco/overcurrent devices in bathrooms [Re: Steve T] #212429 01/06/14 09:49 PM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
I work commercial... even so...

1) Too wet.

2) That's one weird bathroom layout. I wouldn't dream of it since no fireman would ever think to look there when time is critical.

3) Too wet.

More generally, a SERVICE disconnecting means is a critical piece of safety gear and is not to be shoe-horned in to a home.

This is the last item one should think about scrimping on.

Out my way, most SERVICE disconnects will be outside: NEMA3R, even in snow country. When needed, a 'bird house' is set. (micro-roof)

If I were to run into cramped quarters... I'd put the disco outside. It'd usually be quicker, too.

As for the history of various Code provisions... I don't have the interest or the time.


Tesla
Re: Service disco/overcurrent devices in bathrooms [Re: Steve T] #212430 01/06/14 09:51 PM
Joined: Jul 2004
Posts: 9,540
G
gfretwell Offline
Member
Reading the ROP to the 1996 where this came from, I say no to both ideas.

Quote
4-112- (230-70(a)): Accept
Note: It was the action of the Technical Correlating Committee
that this Proposal be referred to Code-Making Panels 1, 2, and 10 for
comment.
SUBMIT'rER: Raymond E. Harper, Seattle, WA
RECOMMENDATION: A new paragraph be added to Section 230-
70(a) to read:
Service disconnecting means shall not be installed in the bathrooms.
A bathroom shall be as defined in Section 210-8.
SUBSTANTIATION: Many bathrooms are not readily accessible
when occupied and the door locked. Servicing the unprotected
conductors in such a confined space with the grounded plumbing
fixtures could be hazardous. This is not a proper location for a
service disconnect. This would be in accord with Section 240-24(e).
PANEL ACTION: Accept.
PANEL STATEMENT: The Panel recommends that the Correlating
Committee review this based on the actions of Panel 10 under
Section 240-24(e)


Greg Fretwell
Re: Service disco/overcurrent devices in bathrooms [Re: Steve T] #212432 01/06/14 09:57 PM
Joined: Apr 2002
Posts: 7,216
HotLine1 Online Content
Member
Thanks for that Greg!
I'm putting that in my book!!


John
Re: Service disco/overcurrent devices in bathrooms [Re: Steve T] #212433 01/06/14 10:23 PM
Joined: Jul 2004
Posts: 9,540
G
gfretwell Offline
Member
All of this stuff is available on the NFPA web site these days.
http://www.nfpa.org/codes-and-standards/document-information-pages?mode=code&code=70

Go down and change the "edition to display" to the cycle you want to look at.


Greg Fretwell
Re: Service disco/overcurrent devices in bathrooms [Re: gfretwell] #212439 01/07/14 12:28 PM
Joined: Feb 2001
Posts: 308
S
Steve T Offline OP
Member
Greg, Thanks. I was looking for that link on NFPA too. Very helpful. I had recalled some language regarding 'access' to the bathroom vs. the damp or wet location substantiation. The 'access' substantiation is more helpful in dealing with the question about passing through the bathroom.

People come up with all kinds of creative ways to layout their basements.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,434
Joined: February 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,901 Are you busy
205,763 Re: Forum
193,875 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3