#21213 01/29/03 12:09 AM
Joined: Jan 2003
Posts: 1
B
big lug Offline OP
Junior Member
How far apart do you staple romex. I'm rewiring my house and was needing some advice. Thanks in advance.

#21214 01/29/03 12:15 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Within 12" of the box and every 54" after that.

2002 NEC 334.30


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#21215 01/29/03 07:12 AM
Joined: Oct 2000
Posts: 5,392
S
Member
code aside,
i staple (insulated) single runs loosley, at every 2' or so. anything more than 2 runs and i use stackers.

the intervention of 'other trades' has intimidated me to this point.

#21216 01/29/03 09:00 AM
Joined: Mar 2001
Posts: 2,056
R
Member
Keep in mind...
If you are using single-gang non-metallic boxes without internal clamps, you have to staple it within 8" of the box. 314.17 (C) ex. I like the stackers also. They make for a nice looking installation.

[This message has been edited by Redsy (edited 01-29-2003).]

#21217 01/29/03 08:35 PM
Joined: Oct 2002
Posts: 210
S
Member
the minimums are with 8" of a NM box without clamps or 12" from a box with clamps and every 4 1/2 fett there after. Never staple on a twist, keep romex flat.

I once had a helper that could not grasp this concept so we had to go to stapling "hammer length apart", I kid you not...

#21218 01/29/03 09:54 PM
Joined: Feb 2002
Posts: 375
G
Member
4' works nicely with usual stud spacing and plywood sizes.