400 amp remote service #211570
10/27/13 08:34 PM
10/27/13 08:34 PM
watersparkfalls  Offline OP
Member
Joined: Mar 2005
Posts: 222
Washington...Not DC
I am going to bring 400 amp service to a remote location, meter only no disco's till they terminate at their locations one to the house the second to the shop; The house has a ufer to establish service, however the shop doesn't have a ufer. Would I be required to establish its service at the remote location and bring 4 wires to the shop or can I still establish service at the shop and use 2 ground rods in lieu of ufer? Thanks sparky

2017 / 2014 NEC & Related Books and Study Guides
Re: 400 amp remote service [Re: watersparkfalls] #211571
10/27/13 09:21 PM
10/27/13 09:21 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,253
Estero,Fl,usa
Two separate buildings can have 2 services off the same drop or "may poled" from a single metered pole in the middle.
I would ask the AHJ how they feel about sending service conductors, building to building after the meter but I can't imagine how it isn't legal.


Greg Fretwell
Re: 400 amp remote service [Re: watersparkfalls] #211583
10/29/13 03:43 PM
10/29/13 03:43 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,997
Brick, NJ USA
If there is no Ufer available, and no footings being installed, then you must use any other available grounding electrode.

With nothing else (Ufer,water,steel,etc) you must install rods, ring, plate.


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,629 Are you busy
186,369 Re: Forum
175,846 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 15 (0.004s) Memory: 0.9519 MB (Peak: 1.0777 MB) Zlib enabled. Server Time: 2018-08-19 21:48:11 UTC